 - NE Nebraska
 - EC
There isn't any wall space to put a panel in that closet however, that was not Bob's point.
I did a walk in closet where every item had it's own cabinet with doors for clothes. So is the room a closet or are the cabinets the closet?
I actually got the architect to change the name of the room on the drawing to dressing room because he wanted a chandelier over a center island (table). The inspection department gave it their OKay....
And if you have a 30 x 36 open space you should have no problem placing a panel there either
Code definition of clothes closet uses the words room or space which does not give us a definite boundary.
240.24 (D) really needs something changed.
Why is clothes closet the only ignitable material that is even mentioned? I have seen panels located in areas that are more of a problem with ignitable material than what a clothes closet presents. What about installing an overcurrent device(s) accepable for class 2 or 3 hazardous locations in a clothes closet? The surface temperatures should never get hot enough to be a problem.
This is just not right as worded. It is a start for what is probably intended but not finished.