twisting wires

Status
Not open for further replies.
The insulation's handy but you could get that from tape.

The true work of a pressure connector is to maintain firm pressure on the conductors comprising the splice, in my opinion.
 
I never did it, but Buchannon crimp barrels are listed for use on current carrying wires and field insulated with tape or the plastic sleeve covers. I have come across many many done this way, some of them burnt up, but then again I have seen lots of cooked up wirenut connections also. I hardly pretwist anymore due to carpal. I put them in a tan twister strait, then let my impact drill and wirenut wrench do the securing. End result = same, the wires are twisted together tightly afterwards. Visual check of the wirenut for overstress is mandatory if you proceed to use my method...
 
I've been in commercial/industrial service for 25 years and I've seen a lot
of failures due to "Loose" un-twisted splices. I can recall at least (9)
instances, where a loose un-twisted grounded conductor damaged/
destroyed equipment. I prefer to learn from the mistakes of others.

My name is Karl, and I'm a Twister. :)
 
I was tought to allways twist my wires together befor putting on a wire nut. Is there a code saying such?

You are not required to twist but would you save more time by not twisting once you consider that a bad connection would mean a call-back and maybe some time spent trouble shooting.

I think it's more cost effective to make good splices on the types of jobs that I do. I have worked for companies that didn't think that way, they would rather have a few repairs. It's your choice.
 
I was tought to allways twist my wires together befor putting on a wire nut. Is there a code saying such?

Smoking!

I think the only purpose of twisting is to ensure that boxes do not become overcrowed. The code has conductor fill rules intended . Section 314.16 requires that boxes and conduit bodies shall be of sufficient size to provide free space for all enclosed conductors.
 
I've been in commercial/industrial service for 25 years and I've seen a lot
of failures due to "Loose" un-twisted splices. I can recall at least (9)
instances, where a loose un-twisted grounded conductor damaged/
destroyed equipment. I prefer to learn from the mistakes of others.

My name is Karl, and I'm a Twister. :)

This is the part that always gets lost.:grin:

No one here is saying when completed the wires should not be twisted, the instructions require it. :)

All some of us are pointing out is that 'pre-twisting' is no better than 'post -twisting' the result is the same, the wires are twisted together and will stay together if the wire nut is removed.
 
Last edited:
Smoking!

I think the only purpose of twisting is to ensure that boxes do not become overcrowed. The code has conductor fill rules intended . Section 314.16 requires that boxes and conduit bodies shall be of sufficient size to provide free space for all enclosed conductors.

No offense but you are clueless on this one. :grin:
 
Read the instructions on the bag of wire nuts.

That said just think about the fact that you do not normally find a loose connection on a splice that has been pretwisted as often as you find loose connections on splices that have not.

If a wire nut is PROPERLY INSTALLED pretwisting is not required
 
I used to pretwist but now rarely do. Once the wire nut starts I like to pull back on each conducter, if one is loose later its probably going to pull out now. Then I finish with nutdriver or Ideal tool.

But I don't have any real objections to pretwisting.
 
I was tought to allways twist my wires together befor putting on a wire nut. Is there a code saying such?

Yes, it is right after the code about what direction the ground lug is supposed to face on a receptacle. UP/down??????
 
Smoking!

I think the only purpose of twisting is to ensure that boxes do not become overcrowed. The code has conductor fill rules intended . Section 314.16 requires that boxes and conduit bodies shall be of sufficient size to provide free space for all enclosed conductors.

??????????????????????????????????????????????????????????????????????????What did he say?
 
Read the instructions on the bag of wire nuts.

Marine,

Check with the manufacturers.
I found each provides a 'torque' requirement
described by saying that the wires must end-up being post-twisted, with the twist showing below the wire-nut skirt.

I agree with iWire basically.
They should end-up being in a post-twisted state,
and stay together when the wire-nut is removed.
:)
 
Wait until the day you are troubleshooting a hot circuit and remove wirenut and have all the conductors fly apart; you'll pre-twist!


AHHHHHHHHH!!!!!!!!!!!!!!!!!!!!!!

No one has said the wires should not be twisted, only that it makes no difference if you do it before or after the wire nut goes on. :)
 
I prefer twisting wires together to make joints... And the reason that I prefer twisting wires is in dealing with MWBC's When one depends on the wire nut to twist as in no twisting required, When the wirenut gets removed, the wires have a tendency to untwist and the lost neutral connection becomes a slight problem. But with pretwisted wire going in a wirenut, the wires don't have such a tendency to untwist.... I also prefer to twist the main circuit conductors first then twist in any taps to fixtures... which also aids in continuity...
 