Dave,
I think that we really have several different 'competitions' and that you are focusing on one of them:
1) How many conductors can be spliced by a device where any one conductor has _direct contact_ with any other conductors in the splice.
2) How many conductors can be spliced by a device in which the attachment to _all_ of the conductors is made by a single operation.
3) How many conductors can be spliced together by a single device which fits in a normal branch circuit junction box.
4) How many conductors can be spliced together by a single device that you buy as a single device.
IMHO you seem to imply that you are looking for  1), but I think that that from the acceptable examples given you are really asking about 2).
If you think about it along the lines of busman's post, the answer to 1) is going to be 3 or 4, at least for reasonable length splicing devices.  Any more conductors, and you will pretty much be guaranteed that some conductors in the set will be connected via an intermediate conductor.  A wire nut that holds 6 conductors will not have all of those conductors touching all of the others.
But the answer to 2) really is quite practical and interesting...how many conductors do you need to prep, orient, and hold in exactly the correct position all at the same time, while attaching the device.  To put a dozen wires under a single crimp, each wire coming out of a separate cable, all aligned...you would almost need a jig to hold the wires together in the first place....
If I were splicing a dozen conductors in a junction box, I think that I would want to use a 'terminal strip' type splice, something that would allow me to make up and attache only one or two of the conductors at a time.