I am working on a small project that during a site visit it was discovered that the Electrician installed PVC underground for Panelboard Feeders and a few branch circuits (to Patient Care Areas).
He was informed that the Branch circuit conduit would need to be abandoned and run overhead in either Healthcare AC Cable or EMT.
My Question stems from the Feeders run Underground in PVC. I am of the opinion that per 517.C.3.1 the PVC feeders are acceptable.
The Engineer is indicating that per 517.19.D That the feeders need to be run in Rigid Underground or EMT Overhead. My stance is this only applies if you ran the Feeder in Metal Conduit or MC or MI cable. Since the Feeders meets the requirement of 517.C.3.1 this installation is acceptable.
Any comment on this would be appreciated.
-Ed