Another dumb Engineers question. How do you identify a AL/CU wire nut by looking at it? Say a # 4 AWG Al to a # 6AWG copper on a 30 amps HVAC circuit?
I don't think I'd try wirenuts for wire that large. A mixed-metal split-bolt (with the divider plate) would be better, or small 2-hole Polaris-type splices.Say a # 2 AWG AL to a # 6AWG CU on a 30 amp HVAC circuit?
Bob,thank you. Just what I was looking for. One more question.
I assume the reducer is insulated? Naturally I will tape.
Well if there is no UL wire nut for AL/CU, your answer confuses me. What is a Polaris Splice?I don't think I'd try wirenuts for wire that large. A mixed-metal split-bolt (with the divider plate) would be better, or small 2-hole Polaris-type splices.
OK that answers my Polaris question. I have seen them and know what you are talking about now. OK 2 Polaris splices, and a larger J-Box than 4 inches.Bob's are good.
Here's another option: insulated dual rated from POLARIS and they are available in a large range of sizes and configurations. Prices aren't too bad either.
Thx got it, responded while you were replying.See my post above yours. :grin:
That's the main disadvantage of Bob's in-line splices, which I have used. I'd like to see a "U-turn" version, sort of like a 2-hole mechanical lug without the stud tab.OK 2 Polaris splices, and a larger J-Box than 4 inches.
On aluminum, yes, especially outdoors, even when not required.One last question. If it were your home; would you use a No-Ox grease?
Yes. Not any Before, but here is the AFTER Pics when the HVAC contractor that installed it 4 years came to repair it. Needless to say he is going to hear from me.got any pics? :grin:
One last question. If it were your home; would you use a No-Ox grease?
That's the main disadvantage of Bob's in-line splices, which I have used. I'd like to see a "U-turn" version, sort of like a 2-hole mechanical lug without the stud tab.
Hey, I wonder if one could cut the tab off of a 2-hole lug and use it as a splice? Legally, I mean.
Yes. Not any Before, but here is the AFTER Pics when the HVAC contractor that installed it 4 years came to repair it. Needless to say he is going to hear from me.
![]()
Where's the disco?
Just to right of the J-Box out of frame. At least all the splices were in plain site and accessible for inspection Huh?Where's the disco?