Yeah better than the expensive way in Court with a toasted house.Good chance to educate him on the Polaris connectors.. or let him keep using big blues so you can get more repair work. :grin:
Yeah better than the expensive way in Court with a toasted house.Good chance to educate him on the Polaris connectors.. or let him keep using big blues so you can get more repair work. :grin:
Where's the disco?
Why not put the disco over the cable through the wall, as we usually do?Just to right of the J-Box out of frame.
That's the main disadvantage of Bob's in-line splices, which I have used. I'd like to see a "U-turn" version, sort of like a 2-hole mechanical lug without the stud tab.
Hey, I wonder if one could cut the tab off of a 2-hole lug and use it as a splice? Legally, I mean.
You strong like bull, you can make the wire 'U-turn'.![]()
Mongo like!Maybe or you could use this one.
http://www.idealindustries.com/products/wire_termination/lugs/lugs_split_bolts_street_light.jsp
How do you identify a AL/CU wire nut by looking at it?
Maybe or you could use this one.
http://www.idealindustries.com/products/wire_termination/lugs/lugs_split_bolts_street_light.jsp
You sure you have 4AWG and 6AWG - I was expecting larger j box just to be able to bend the #4, and getting them to fit in a blue wire connector may not be impossobile but is not going to be easy. I see they did a fine job of bonding to the box also:roll:Yes. Not any Before, but here is the AFTER Pics when the HVAC contractor that installed it 4 years came to repair it. Needless to say he is going to hear from me.
![]()
Hey Bob I like that one. Will it fit in a 4 inch J-Box?
Chalmuit to be honest I was guessing at the size. So I went and measured it.What about wire fill? If all the conductors were #6, you would need 25 in?. The box shown is only 31.8 in?. So, 3 #2's (L-L-G) and 2 #6's (L-L) would be more in? than 31.8 in?.
Well that is what Bob and I discussed briefly, we do not know that a AL/CU wirenut exist. That is what sent the red flag up when I seen how the contractor fixed it. I was not sure so that is why I started this thread.I have used the purple wirenut before. .
Well that is what Bob and I discussed briefly, we do not know that a AL/CU wirenut exist.
They're purple.How do you identify a AL/CU wire nut by looking at it?
John you are correct, I thought the Ideal 65s were only listed for AL to AL or CU to CU.
http://www.idealindustries.com/products/wire_termination/twist-on/twister_al-cu.jsp
They're afraid we'll use them.Anyone know why they don't make the purples in Larger sizes?
Anyone know why they don't make the purples in Larger sizes?
Once you have conductors larger than #6 you will need boxes sized by raceway sizes instead of conductor volumes. See 314.28(A).What about wire fill? If all the conductors were #6, you would need 25 in?. The box shown is only 31.8 in?. So, 3 #2's (L-L-G) and 2 #6's (L-L) would be more in? than 31.8 in?.