Hello,

I know there must be a thread on this somewhere but I can't find one. If someone can point me in the right direction I would appreciate it.

Residential 200A 1 Phase service
1 panel
#4 GEC from panel to well casing
Copper water pipes need to be bonded (not used as GEC)
250.104 says I can "bond to the GEC where of sufficent size"

I forgot to hit the copper water pipes on my way by with the GEC. Can I run #4 from the cold water pipe to the GEC or do I have to go all the way back to the panel?

Thanks,
Andy
 

ZZDoug

Member
Location
North Dakota
Surprised nobody has answered this after 2 days. You can simply tap off the existing GEC as per 250.64(C)(1) with either cadweld or irreversible crimp. Thats assuming your #4 GEC is correct size, you didnt give enough info for that......
 

ceb58

Senior Member
Location
Raeford, NC
Hello,

I know there must be a thread on this somewhere but I can't find one. If someone can point me in the right direction I would appreciate it.

Residential 200A 1 Phase service
1 panel
#4 GEC from panel to well casing
Copper water pipes need to be bonded (not used as GEC)
250.104 says I can "bond to the GEC where of sufficent size"

I forgot to hit the copper water pipes on my way by with the GEC. Can I run #4 from the cold water pipe to the GEC or do I have to go all the way back to the panel?

Thanks,
Andy

Surprised nobody has answered this after 2 days. You can simply tap off the existing GEC as per 250.64(C)(1) with either cadweld or irreversible crimp. Thats assuming your #4 GEC is correct size, you didnt give enough info for that......

Why did he not give enough info? 200amp service. By 250.66 A it could have been #6cu or #4al
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Surprised nobody has answered this after 2 days. You can simply tap off the existing GEC as per 250.64(C)(1) with either cadweld or irreversible crimp. Thats assuming your #4 GEC is correct size, you didnt give enough info for that......
There is no rule that would require the use of an irreversible crimp or a cadweld to make this tap connection to the GEC.
 

gndrod

Senior Member
Location
Ca and Wa
Hello,

I know there must be a thread on this somewhere but I can't find one. If someone can point me in the right direction I would appreciate it.

Residential 200A 1 Phase service
1 panel
#4 GEC from panel to well casing


I forgot to hit the copper water pipes on my way by with the GEC. Can I run #4 from the cold water pipe to the GEC ?

Thanks,
Andy

Yes. [250.70] bond is permitted.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
There is no rule that would require the use of an irreversible crimp or a cadweld to make this tap connection to the GEC.
Don, there is a graphic similar to this that I always wondered about. where the GEC to the water pipe is tapped to 2 panels. I always thought these had to have irreversible crimps. Am I correct? I will post the graphic.

ry%3D480
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Dennis,
In the question in this thread, the conductor is not a GEC, but a bonding conductor to the interior metal water piping system as required by 250.104.

As to your question, 250.64(D)(1) clearly permits the use of other than an irreversible connection for a grounding electrode conductor tap.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There is no rule that would require the use of an irreversible crimp or a cadweld to make this tap connection to the GEC.

Dennis,
In the question in this thread, the conductor is not a GEC, but a bonding conductor to the interior metal water piping system as required by 250.104.

As to your question, 250.64(D)(1) clearly permits the use of other than an irreversible connection for a grounding electrode conductor tap.

Don is there a specific code section that permits this tap from the GEC to bond the water pipe? 250.64(D)(1) only covers services and I agree that a split bolt would also be permitted for those taps.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
As to your question, 250.64(D)(1) clearly permits the use of other than an irreversible connection for a grounding electrode conductor tap.

Don I don't see that section specifically allowing a tap to be splice. If the GEC is continuous into one panel then I can see a split bolt to the first panel.
 

Smart $

Esteemed Member
Location
Ohio
Don is there a specific code section that permits this tap from the GEC to bond the water pipe? 250.64(D)(1) only covers services and I agree that a split bolt would also be permitted for those taps.
Not Don, but yes...
250.104 Bonding of Piping Systems and Exposed Structural Steel.
(A) Metal Water Piping. The metal water piping system shall be bonded as required in (A)(1), (A)(2), or (A)(3) of this section. The bonding jumper(s) shall be installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible.
(1) General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3).


[2 & 3 omitted for brevity; covers multiple occupancies and buildings]
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Don I don't see that section specifically allowing a tap to be splice. If the GEC is continuous into one panel then I can see a split bolt to the first panel.

If you're referring to your graphic the GEC ends and the two taps are bonding jumpers. Therefore the GEC is not spliced at all. If the first switch had the same size tap conductor (as the GEC) then I would call that a splice.
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not Don, but yes...

250.104 Bonding of Piping Systems and Exposed Structural Steel.
(A) Metal Water Piping. The metal water piping system shall be bonded as required in (A)(1), (A)(2), or (A)(3) of this section. The bonding jumper(s) shall be installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible.
(1) General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3).


[2 & 3 omitted for brevity; covers multiple occupancies and buildings]
Does it have to be irreversible or compression type?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Don I don't see that section specifically allowing a tap to be splice. If the GEC is continuous into one panel then I can see a split bolt to the first panel.
I don't know why you would need to make a splice to connect a tap conductor. I never said you could make a splice without using some type of irreversible connection, I only said you can tap to the GEC without using an irreversible connection.
 

Smart $

Esteemed Member
Location
Ohio
Does it have to be irreversible or compression type?
No. See 250.8 for types of connection permitted for a bonding conductor.

Why would it have to be irreversible? The only rule that requires that type of connection is the one for the GEC. The conductor to the interior water pipe is not a GEC.
That rule [250.64(C)] is not for GEC connections. It is for wire-type GEC splicing.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't know why you would need to make a splice to connect a tap conductor. I never said you could make a splice without using some type of irreversible connection, I only said you can tap to the GEC without using an irreversible connection.

In my eyes if the gec does not terminate at the panel then the tap conductors are splices.
 

Smart $

Esteemed Member
Location
Ohio
In my eyes if the gec does not terminate at the panel then the tap conductors are splices.
But the continuous requirement is for GEC conductors, not GEC tap conductors.

End of 250.64(D)(1)...
... The tap conductors shall be connected to the common grounding electrode conductor by exothermic welding or with connectors listed as grounding and bonding equipment in such a manner that the common grounding electrode conductor remains without a splice or joint.
 