I have a fight with a chief electrican of a facility, and maybe also with the AHJ. This facility has installed a separate ground rod at every 480:208 volt transformer in a large facility (250,000 square feet). We inspected all the transformers, and most of them have a ground rod, no bond from the ground bus of the transformer to the primary ground bus or the grounding electrode system for the building, and no connection to building steel or water pipe. All of the ground rods are driven through a hole in the basement slab, into presumably dry soil - useless. Some transformer secondaries are not grounded or bonded at all, and they do admit these are noncompliant (and dangerous!). As I was photographing these ground rods, the electrician was saying that the AHJ instructed him to do it this way - a separate ground rod at each transformer. I was trying to explain to the electrician the problems that could be caused by this, he wants me to quote chapter and verse from the code where this isn't allowed. All of these transformer secondary grounds should be bonded together and to the main building system ground.
The problem is the Code doesn't come out and say this isn't allowed in plain english, it implies it several places. I'm trying to zero in on the key paragraphs that make the best case. I'm citing the 2008 NEC.
250.30(A)(7) doesn't help: Exception #1 allows separately derived systems to use any of the electrodes identified in 250.52 if building steel and water pipes are not available. It says nothing about bonding this darn ground rod to the main building ground. The AHJ is likely to hang his hat on this paragraph and say that's that.
250.4(A) (1) and (2) give us no ammunition, since they talk about "connecting to earth".
250.4(A)(3) and (5) require cases to be bonded, and (5) specifically says the earth is not an effective ground fault current path. However they could argue that there is no current between a separately derived system and the service entrance if there is a fault on the separately derived system.
250.50 requires all ground rods "that are present" to be bonded together to form an effective ground fault current path. That comes close.
250.58 requires a "Common Grounding Electrode" but does not specifically mention separately derived systems.
I wish there was an article that says "multiple separately derived systems shall be connected to a single common grounding electrode that is bonded to the building service grounding electrode system" but there is no such paragraph. 250.30(A)(4) doesn't say this.
What is worse, this is a hospital. Small differences in potential between two 120V systems could have deadly consequences. An amp of ground current, due to a nearby substation, could produce tens of volts between two ground rods, enough to stop a patient's heart if two machines are plugged into different separately derived systems and then connected to the patient.
The problem is the Code doesn't come out and say this isn't allowed in plain english, it implies it several places. I'm trying to zero in on the key paragraphs that make the best case. I'm citing the 2008 NEC.
250.30(A)(7) doesn't help: Exception #1 allows separately derived systems to use any of the electrodes identified in 250.52 if building steel and water pipes are not available. It says nothing about bonding this darn ground rod to the main building ground. The AHJ is likely to hang his hat on this paragraph and say that's that.
250.4(A) (1) and (2) give us no ammunition, since they talk about "connecting to earth".
250.4(A)(3) and (5) require cases to be bonded, and (5) specifically says the earth is not an effective ground fault current path. However they could argue that there is no current between a separately derived system and the service entrance if there is a fault on the separately derived system.
250.50 requires all ground rods "that are present" to be bonded together to form an effective ground fault current path. That comes close.
250.58 requires a "Common Grounding Electrode" but does not specifically mention separately derived systems.
I wish there was an article that says "multiple separately derived systems shall be connected to a single common grounding electrode that is bonded to the building service grounding electrode system" but there is no such paragraph. 250.30(A)(4) doesn't say this.
What is worse, this is a hospital. Small differences in potential between two 120V systems could have deadly consequences. An amp of ground current, due to a nearby substation, could produce tens of volts between two ground rods, enough to stop a patient's heart if two machines are plugged into different separately derived systems and then connected to the patient.