is there any issue using 240 water heater element on 208 service?
is there any issue using 240 water heater element on 208 service?
That is how it will perform, but the rating did not change. A transformer (480 volt primary) rated for 150 KVA does not become a 75 KVA-rated transformer, just because you choose to supply it with a 100 amp breaker. A 5 HP motor does not become a 3 HP-rated motor, just because you choose to use it to supply a 3HP mechanical load. A heating element rated for 4500 VA at 240 volts is still rated for 4500 VA, even if you choose to supply it with 208 volts, or unless the manufacturer has given it a separate rating at different voltages.a 4500 watt element rated at 240 volts is really 3380 watts at 208 Volts.
Yeah we did, and I still think my way is the right way.T
Didn't we do this dance once already, recently?![]()
That doesn't make it less efficient.No code issues, unless the manufacturer's literature specifically states that it is for use only on a 240 volt system. But there is an operational concern. It will operate at 75% efficiency, and will heat water that much slower. The 75% is based on (208/240) squared.
a 4500 watt element rated at 240 volts is really 3380 watts at 208 Volts.
I would. If the unit only said 4500 watts and that it can operate at 240 volts or 208 volts, would you change your tune?If the unit stated 208/240 V and 3380/4500 watts would you change your tune?
Nope. Simply because it can't operate at 4500 watts at both voltages.I would. If the unit only said 4500 watts and that it can operate at 240 volts or 208 volts, would you change your tune?![]()
I would agree the wording may not be there but you asked would I change my tune and I said Nope.....:grin:But the key word in the code article is "rating," not "OPErating." I am speaking about a circumstance in which the only rating placed on the item is a 4500 VA rating. I would certainly make the same design decision that you are describing, but I submit that the code, as written, does not require me to do so.
is there any issue using 240 water heater element on 208 service?
Technically no....If the unit's nameplate states 240V, and it is id'd on the nameplate as UL, can you operate it at 208V per the NEC?
Yeah we did, and I still think my way is the right way.If the unit stated 208/240 V and 3380/4500 watts would you change your tune?