duftelectrical1978
Are laundry branch circuits (120 volt 20 amp) required to be AFCI protected.
			Welcome to the forum.
Under the 2008 a laundry area is not one of the areas listed in 210.12(B) so no AFCI protection is required for outlets in the laundry area.
Chris
Chris, The ahj in Colorado is using the NEC handbook and in the authors notes it lists around 5 areas that are note required to be afci protected and laundry rm. is not one of them. Therefor it is required according to him. I then asked why dispoals, dishwashers, microwaves, sump pumps, sewage lift stations and the like are not required. He didn't know. How is a laundry rm. considered a simular area in article 210.12(B). He said its not, but he is going off the authors notes in the handbook. I informed the author of the handbook unlickly was on the code making panel for this code change. Do you think this is out of the ordanary.
Only the NEC is adopted as law. The Handbook, while it contains the NEC, also has commentary. The commentary is not the NEC, nor part of the NEC. The commentary is only the opinion of the authors of the Handbook (albeit very helpful opinion, but only opinion about the enforceable language none the less).The ahj in Colorado is using the NEC handbook and in the authors notes it lists around 5 areas that are note required to be afci protected and laundry rm. is not one of them. Therefor it is required according to him.
Here, he is admitting that the NEC language doesn't support his position. This is where he should stop.How is a laundry rm. considered a simular area in article 210.12(B). He said its not, but he is going off the authors notes in the handbook. I informed the author of the handbook unlickly was on the code making panel for this code change. Do you think this is out of the ordanary.
IMO it depends on the location. In a separate laundry room then no AFCI required, but around here many washers and dryers are installed in a hall closet outside of the bedrooms. That would require AFCI protection since closets are on the list that jumper posted.
So would the closet be a "laundry area" as contemplated in 210.52(F) or is it just a closet with a clothes washing machine in it?
If it's not considered a laundry area would 210.52(F) even apply? If it is considered a laundry area to comply with 210.52(F) then would 210.12(B) apply to the laundry area?
Pete
Pete
A closet must have afci protection. So if the washer/dryer is in a closet it requires afci protection because it is not a laundry room it's a closet with a washer/dryer in it.
Why would a "closet" that contains a washer and dryer not be a laundry area and a "Room" that contains the same equipment be a laundry area?
210.52(F) does not require the laundry to be located in a room but in an area.
Chris
Well a closet is a closet right? I can see your point though. ....
Infinity posted they call it a closet where he is. I guess it would depend on whether or not you define it as a closet or laundry area.
I've seen some pretty big closets.... big enough to put my kitchen and dining room in.
I guess ultimately, as with many interpretations, the AHJ has to make the call as to whether or not the location is a closet or laundry area or both...
Pete
What enforceable language do you use to determine that a space, with hot and cold water hookups, exhaust venting, gas line (if needed) and sewer, all sized for the common dwelling laundry machines, that a space is no longer a closet and is now a room or area?IMO it depends on the location. In a separate laundry room then no AFCI required, but around here many washers and dryers are installed in a hall closet outside of the bedrooms. That would require AFCI protection since closets are on the list that jumper posted.
Understand what I'm asking. There is a dwelling space with all the laundry mechanicals installed. Those are planned to be there. The plan will designate this as a Laundry.I don't really see a definition either way. Take the machines out and you have a hall closet, put them in and now you have a room?