Yes. The IAEI Power Point presentation only shows kitchens, bathrooms and garages as not requiring AFCI protection.
Do I think that they wanted to exempt GFCI's or related circuits? Yes. But that is not what the code says.
Read the commentary. It only addresses kitchens, bathrooms, unfinished basements, garages and outdoors. Laundry is not listed.
So any teaching material should be ignored? How do you feel about the commentary?
While Ohio used the PP to teach the changes in the 2008 NEC these are my opinions not the state's.
You have confused me.:-?
You state that AFCI is required in laundry areas, because of commentary and IAEI PP, but then you say this is your opinion and not the states.
When you inspect, what do you enforce? Code or commentary?