jxofaltrds
Retired ESI
- Mike P. Columbus Ohio
- Creator
So our EGC's aren't true grounds but their little ground spike is?
Also, it's a violation of the NEC not to bond all grounding electrodes together.
It appears that somebody didn't get the memo:
The original question was whether connection to an isolated stake in the ground, or connection to the GEC system by way of the grounding jack in a receptacle were allowed by Code.
Some posts were relevant to this, others were concerned with whether grounding the body was "weird", a word I remember from high school.
As to Code, and other electrical questions:
Shielding often uses some of the conductive materials that are used for grounding. The shielding is usually for radio frequency and higher. Static discharge is another function.
The post that mentioned the routine use of grounded wrist straps in industry; can you tell me what they were grounded to? It occurs to me that the NEC question may have already been answered, since these are mass produced and used in computer manufacturing, and any process where static charge could damage the product. The wrist straps contain a built-in 1 megohm resistor, so that they are protected from an accidental energizing.
The providers of devices, as well as the researchers, are not thoroughly familiar with the questions about grounding that this forum was created to deal with, stemming from Mike Holt's books. That is why I am asking these questions, so I can pass on the best opinions to the researchers and product providers.
Some think the isolated stake is the better, or purer, connection to earth. Others assume the GEC system is fine. The health effects results would seem to confirm that either works.
But to get back to the short metal stake in the ground, I do not think it is correct to call it a grounding electrode, since it is not part of the building electrical system, and is not purposed to ground an electrical device, in NEC terms. So the NEC question is, is it even covered by the NEC, assuming that there are no metal parts likely to be accidentally energized? I solicit opinions about this.
Someone mentioned metalized threads and the danger of being in contact with them if they are grounded. The cloth I am using ("anti-static fabric") recommended has carbon fibers woven in, and has high enough resistance to keep currents at about 1 mA or less. The metalized (silver) fabric he mentioned has a much lower resistance and must be used with a resistor or mA fuse.
ALL CONDUCTIVE CONTACT WITH THE BODY SHOULD BE DISCONTINUED IF THUNDERSTORMS ARE IN THE AREA. But this applies to any contact with grounded metal in the building, as well as to computers and sensitive instruments. So this is not a factor as far as my question goes. I notice that the product info sheets contain this safety warning.
If anyone has opinions on either safety or NEC (should be the same, but not always), please contribute your opinion. We are close to getting this solved.
See next post about "weird", etc.
I think that the cord violations 400.7. I think 400 applies because it is plugged into a receptacle outlet.
I have a problem with #4 in the picture because of a paralled path for the EGC but can not find a NEC violation.
The 'ground rod' (8-10") IMHO does not fall under the NEC. If it does not meet 250.52(A)(5) so 250.53 does not apply.
Also some of the FAQ scare me. http://www.earthinginstitute.net/index.php/faq