I felt like I couldn't pigtail a piece of 12 to 14 and use a 20 amp breaker, nor could I use a 12 hot and 14 neutral on a 20 amp breaker, 12 all the way both before and after the resistance.

The 12 would be the heat sink for the breaker but the 14 would still be wrong.
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
I felt like I couldn't pigtail a piece of 12 to 14 and use a 20 amp breaker, nor could I use a 12 hot and 14 neutral on a 20 amp breaker, 12 all the way both before and after the resistance.

The 12 would be the heat sink for the breaker but the 14 would still be wrong.

If a smaller grounded conductor were acceptable, you would see NM and MC made with a #12 phase conductor and a #14 white, With all the large projects that are built it would save millions over time.

I noticed some proponents of a smaller grounded conductor have not posted after logic and code sections were posted.:grin: some people can't accept being wrong.
 