Bob.
Grounded conductors generally are not connected to an overcurrent device. If a branch circuit grounded conductor makes contact with an equipment ground conductor and/or a grounded surface, the circuit breaker/fuse for that circuit will not open. Therefore groundfault current does not flow on the grounded conductor
No ground fault current does not normally flow on the grounded conductor, but short circuit current will.
No the grounded conductor does not directly connect to the OCP in most cases but regardless of that the OCPD is intended too, and does protect the grounded conductor from overload / overcurrent.