Inspector is incorrect since you have a grounded box and a self-grounding receptacle.
cell phone was broken up with inspector . nice guy the inspectoir but some times i wonder what code he is reading.
it is my undrstanding you do not need a bonding wire from a self grounding rec to the box if using ac cable.
now i may agree with him on the gfi but it can be installed if you mark it on the plate some how that there is no egc
1900 box with a single adapter cover
Are we talking about a raised cover ? If so i agree with inspector. Not sure of code number but i see the hazard if cover came loose
What is a single adapter cover? If your receptacle is cover-mounted you will have to install an equipment bonding jumper from the box to the receptacle unless the box and cover combination are listed as providing satisfactory ground continuity between the box and receptacle . 250.146 (A)
250.146 B) Contact Devices or Yokes. Contact devices or yokes designed and listed as self-grounding shall be permitted in conjunction with the supporting screws to establish the grounding circuit between the device yoke and flush-type boxes. ( not bonding jumper is required)
A receptacle designed with a listed spring-type grounding strap. The
strap that holds the mounting screw captive establishes a grounding circuit and
eliminates the need to provide a wire-type equipment bonding jumper to the box, in accordance with 250.146(B).
the raised would not be count because the 8/32 screws are not threded through cover to the to the box
so even if it was a self grounding receptacle you need the grounding jumper:roll:
If your receptacle is cover-mounted you will have to install an equipment bonding jumper from the box to the receptacle unless the box and cover combination are listed as providing satisfactory ground continuity between the box and receptacle. 250.146(A)
250.146(A) is not the right code section for self grounding devices.
Look at 250.146(B)
I agree but I said if the receptacle was cover mounted 250.146(A) would apply. I have never heard a plaster ring called a single adapter cover in which case 250.146(B) would address the self-grounding device.