IEEE Std C57.13.3-2005
7. Exceptions to grounding
Exceptions to grounding are permissible and sometimes required where advantages obtained by not grounding (in certain instances or in certain types of installations) are considered to outweigh the safety or other advantages obtained by grounding. Such exceptions should comply with the recommendations of the NEC. Grounding exceptions are generally permissible under the following circumstances:
a) If the primary windings of instrument transformer circuits are connected to circuits of less than 1000 V with no live parts or wiring exposed or accessible to other than qualified persons, the circuits may not be grounded.
b) For instrument transformer cases, the cases or frames of CTs may not be grounded if the primary windings are not over 150 V to ground and are used exclusively to supply current to meters.
c) Cases of instruments, meters, and relays operating at less than 1000 V on switchboards having exposed live parts on the front of panels are not usually grounded. Mats of insulating rubber or other suitable floor insulation are provided where the voltage to ground exceeds 150 V.
d) Instruments, meters, and relays, whose current-carrying parts operate at voltages to ground of 1000 V and over, are isolated by elevating them or protecting them by suitable barriers, grounded metal or insulating covers, or guards. In such situations, the cases are not usually grounded.
WARNING
When exceptions to grounding, as suggested here, are considered for implementation, the reader should make certain to meet requirements stipulated in the NEC and NESC. Article 90.2 (A) of the NEC lists the installations that are covered by the Code, and Article 90.2 (B) lists the installations that are not covered by the Code. For immediate reference of the readers, Article 90.2 of the NEC is reproduced in Annex C.