Do wall spaces behind appliances (fridge, range, DW, etc.) in a dwelling-unit kitchen require a 120v 15- or 20a receptacle per 210-52(A)(2)(1)?
 
Do wall spaces behind appliances (fridge, range, DW, etc.) in a dwelling-unit kitchen require a 120v 15- or 20a receptacle per 210-52(A)(2)(1)?

...are you trying to apply a 'general provision' to an entire section? If so, keep reading sec 210.52. Look at fig 210.52(C)(1)
 
Do wall spaces behind appliances (fridge, range, DW, etc.) in a dwelling-unit kitchen require a 120v 15- or 20a receptacle per 210-52(A)(2)(1)?

...you say your talking about 'wall space,' than I think you need to explain the exact situation your questioning! Who puts a dishwasher in an 'open wall space' (no counter to left or right, just walls:-?)
 
...you say your talking about 'wall space,' than I think you need to explain the exact situation your questioning! Who puts a dishwasher in an 'open wall space' (no counter to left or right, just walls:-?)


OK; the exact situation is:

You're having your final done. The appliances are two weeks out, and not part of you contract. There's an opening between the cabinets for the DW, but it's not installed. Can the inspector require a receptacle there because it's a 24" wall space?




















And I will ask again, in vain hopes that someone will answer:


WHAT DO COUNTERTOPS HAVE TO DO WITH CONSIDERING IT A WALL SPACE REQUIRING A RECEPTACLE?
 
OK; the exact situation is:

You're having your final done. The appliances are two weeks out, and not part of you contract. There's an opening between the cabinets for the DW, but it's not installed. Can the inspector require a receptacle there because it's a 24" wall space?




















And I will ask again, in vain hopes that someone will answer:


WHAT DO COUNTERTOPS HAVE TO DO WITH CONSIDERING IT A WALL SPACE REQUIRING A RECEPTACLE?

NO. Yes you WOULD pass.
It is not wall space.
 
480 << can't capitalize the 4 it =$:roll:

never mind misread again

I did have an inspector once try to apply 210.52(A)(1) once to these spaces but all I got to say it was a bad beat with the state on my side.:grin:
 
Last edited:
OK, let's try this:


Does this 24" space require a receptacle?:

24inch1.jpg



What about this one?:

24inch2.jpg
 