mivey
That should be Art 382Oh it's made by SouthWire! They cite NEC code Art. 322 Flat Cable Assemblies.
The NEC does not recognize it as an appliance so it ain't as far as the NEC is concerned and that is what matters. It is, however, an assembly of parts that is intended to be used by an appliance.Respectfully, you claim its not an appliance, however, a NRTL, not Joe-Bob's Lab, has asserted the claim in an official control report.
Okay, Listing in itself may not have to be recognized, however the right should not extend to claim something offically cited as something else.
Can I call a cord an outlet receptacle just because it has a 5-15P on the end of it? I could if the rule applys to an AHJ to call any listed product whatever they deem suitable to fit a citation.
I suppose I could call an outlet an EXTENSION CONNECTOR of the fixed wiring and apply a different set of rules to it.
So, we'll agree an AHJ can call a product, Listed or not, anything they want.
Is this correct?
We can rename the cord a Transfer-Device, does this make it more or less acceptable.
And you can demonstrate this with what citation(s)?The NEC does not recognize it as an appliance so it ain't as far as the NEC is concerned and that is what matters.
Because it does meet the definition as spelled out in the NEC. It does not perform functions like those given by example and it is not utilization equipment with a purpose similar to those given by example.And you can demonstrate this with what citation(s)?
And it includes overcurrent, GFCI, and arc fault protection in case something does happen.This is a "new" product coming on the market.
FLATWIREREADY
It personally scares me far more than using a power supply cord that can be unplugged at anytime and replaced with same very easily.
I could envision a HO cutting into this or nail into it and damage it, causing a difficult replacement.
In your opinion.Because it does meet the definition as spelled out in the NEC. It does not perform functions like those given by example and it is not utilization equipment with a purpose similar to those given by example.
In your opinion.
Is this correct?
Article 100 "appliance" is a one word term.Al, how is that an opinion when Article 100 clearly tells us appliances utilize power?
Well, this is where the scale tips, in my opinion.
In the rush to, or adherence to, 400.8(1), the very language of the listing is dismissed out of hand as irrelevant or below Code minimum.
Until the ambiguity of the listing can be removed, IMO, 110.3(b) guides me to believe 400.7 is in play.
I agree it is an assembly. It is just not an appliance. It is an assembly that is intended to be used by an appliance. Thus it is an appliance assembly.In your opinion.
What citation do you use to deal with "appliance assembly", if, in fact it is an appliance assembly. What citation demonstrates that it is not an appliance assembly, if, in fact it is not an appliance assembly.
Can you show me a reference that says "appliance assembly" is not a two word term, or for that matter a reference that says an appliance assembly is not part of an appliance.
The wording is ambiguous and requires further enforceable language to remove the ambiguity.
AgreedEither way, this is an EXTENSION supplied from the existing premise wiring circuit, not from the back, from the front.
Because this method is not forbidden to substitute. I am also curious if these 382 devices have regular receptacles to accept appliance cords?Does this substitute the structures wiring as defined in 400.8. I know, this is not classified as a flexible cable/cord, but it is still a premise being argued here that jumping from the front of the circuit is a substitution. How is this really different than using a cord to EXTEND from the outlet. It seems to allow the "action" in 382.10(A).
Get a code section for the PowerBridge type device without a section that excludes it from substituting and you are good to go.For discussion omit the highlight, only to allow this as an observation and possible proposal to the use of a proper cord to acheive the same result of extension from an existing outlet as cited in Code. I don't need to be reminded this article is specific to NM Extensions only, I get it.
Oh, come on, you can do better than that. This is the NEC Forum after all.Who needs a code reference?
Didn't say it was an appliance. I'm saying it is something else that is recognized as an appliance assembly. That much I get from 110.3(B). Tell me what it is or isn't by the Code. Demonstrate that this is not part of an appliance. Demonstrate, by Code, that it IS something.The kit is not a complete appliance.
Why should I kid. The language is not mine. I'm trying to make sense of it.You are kidding me right?
Appliance is not the end of the phrase. Appliance appears as a modifier to Assembly.In Wall Electrical Appliance Assembly
It might be.I agree it is an assembly. It is just not an appliance. It is an assembly that is intended to be used by an appliance. Thus it is an appliance assembly.
I haven't changed the word order. It is only as it is written by a NRTL.You can play with the word order but one of the results does not fit the NEC definition.
You'd think so, but there are too many versions of "common sense" here participating in this thread.You can play around but common sense should prevail . . .
There sure is ambiguity, otherwise we wouldn't be here.There is no ambiguity of the listing, the listing says what it says and the NEC says what it says.