Awww. Shucks. My ruse is seen through . . .Color me doubtful. :grin::grin:
Awww. Shucks. My ruse is seen through . . .Color me doubtful. :grin::grin:
It is evidently not an approved branch extension method. It is not an approved method to substitute for fixed wiring.Tell me what it is or isn't by the Code. Demonstrate that this is not part of an appliance. Demonstrate, by Code, that it IS something.
The NEC is silent about "appliance assembly", which produces no understanding one way or the other.
The OUTLET and INLET are not listed from PowerBridge as separate components but as a KIT. They have specific labeling and instructions to the listed use as an IN WALL ELECTRCIAL APPLIANCE. Appliances are allowable to be energized by cord-sets.
And, by in play, I mean it is one of the possible ways that the Code comes into play, not the only way.There is no ambiguity of the listing, the listing says what it says and the NEC says what it says.Until the ambiguity of the listing can be removed, IMO, 110.3(b) guides me to believe 400.7 is in play.
Who needs a code reference? The kit is not a complete appliance.
Take a common situation: a UL-listed wire, a UL-listed receptacle, and a UL-listed box. Heck, we'll even put a UL-listed cord grip in the package. Put them together, and you have a very nice, but unlisted extension cord assembly. (Search this forum and you'll find a few discussions as to whether it's even legal too )
As for the various forms of 'flat wire,' in each case the manufacturers went to the code committees and had the code ammended before they marketed the products. FWIW, UL refused to list them until there was a provision in the NEC for the new 'methods.' If you want to discuss 'flat' wire, I suggest a new thread for another topic.
Edit: I've reconsidered. The wrong question is being asked.
110.8 says only recognized methods will be permitted. "Recognized methods" are those described in Chapter 3 (Articles 300-399). Flexible cords and extension cords are not mentioned as an approved method.
So the question is not 'where is this forbidden,' but rather 'where is it allowed.' One cannot prove a negative - and there most certainly will not be a citation for something that does not exist.
Glad to. It comes from the Intertek "ETL Listed Mark Directory" search results for the PowerBridge product. HD Products Inc. DBA PowerBridge. click hereCan you help me out and let me know where appliance assembly came from?
I like your thinking, Bob. Maybe I've gone about this all wrong. :roll:I suppose you would tell me there is no NEC definition for "in wall electrical appliance" making the NEC definition of "appliance" out of bounds.
And just what citation from the Code unambiguously states this about the PowerBridge?It is . . . a lot of parts put together as a packaged substitute for something else.
It is a substitute for the receptacle required by 210.50(B)And just what citation from the Code unambiguously states this about the PowerBridge?
(B) Cord Connections. A receptacle outlet shall be installed
wherever flexible cords with attachment plugs are
used. Where flexible cords are permitted to be permanently
connected, receptacles shall be permitted to be omitted for
such cords.
Instead of installing the receptacle required by 210.50(B) you have installed the PowerBridge instead. That is a substitution.A couple attempts at a rebuttal to the idea that the PowerBridge cord violates 400.8(1):
(1) The PowerBridge kit as a whole is a controller: "A device or group of devices that serves to govern, in some predetermined manner, the electric power delivered to the apparatus to which it is connected." As such, according to the definition of "Premises Wiring System", the NM wiring in the PowerBridge kit is not part of the Premises Wiring System. Therefore the cord in the PowerBridge kit is not substituting for "the fixed wiring of a structure".
(2) I believe Don commented that male and female plug ends are available for flexible conduit. As such the inlet in the kit could be connected to a receptacle with flexible conduit. This flexible conduit would not be "fixed" wiring, so the cord is not substituting for "fixed wiring".
Cheers, Wayne
Look at the first sentence of 210.50. 210.50(B) has no information about where the receptacle outlet has to be. If the receptacle outlets required by the first sentence of 210.50 are present, no more are required. Adding the PowerBridge is not substituting for anything by this citation of yours, IMO.It is a substitute for the receptacle required by 210.50(B)Instead of installing the receptacle required by 210.50(B) you have installed the PowerBridge instead. That is a substitution.B) Cord Connections. A receptacle outlet shall be installed herever flexible cords with attachment plugs are used. Where flexible cords are permitted to be permanently connected, receptacles shall be permitted to be omitted for such cords.
2008 NEC
210.50 General.
Receptacle outlets shall be installed as specified in 210.52 through 210.63.
The attachment plug must be able to reach the receptacle, otherwise it could be in China.Look at the first sentence of 210.50. 210.50(B) has no information about where the receptacle outlet has to be. If the receptacle outlets required by the first sentence of 210.50 are present, no more are required. Adding the PowerBridge is not substituting for anything by this citation of yours, IMO.
Well, maybe not in China. Just where required by 210.52 thru 210.63.The attachment plug must be able to reach the receptacle, otherwise it could be in China.
It is a substitute for the receptacle required by 210.50(B)
Instead of installing the receptacle required by 210.50(B) you have installed the PowerBridge instead. That is a substitution.
McGraw's NEC Handbook states it plainer than I must have beenWell, maybe not in China. Just where required by 210.52 thru 210.63.
Show me the requirement that the cord attached to a given appliance (the wall mounted TV) must have a receptacle outlet installed within reach of that cord's attachment plug.
One certainly can install the receptacle outlet, however, it is not a required receptacle outlet unless it just happens to be in the place described by 210.52 thru 210.63 and the original installation of the Premises Wiring (System), under this NEC, happened to be incomplete and nobody caught it.
Part (B) states that if flexible cord is used to connect portable lamps or appliances, stationary equipment to facilitate frequent interchange, or fixed or stationary appliances to facilitate removal or disconnection for maintenance or repair, the cord ?shall be equipped with an attachment plug and shall be energized from a receptacle outlet.?
It should be noted that the cords referred to under this section are the cords attached to the appliance and not extension cords supplementing or extending the regular supply cords. The use of an extension cord would represent a conflict with the requirements of the Code in that it would serve as a substitute for a receptacle to be located near the appliance, thereby violating 210.50(B).
Extension cords are intended for temporary use with portable appliances, tools, and similar equipment which are not normally used at one specific location.
The Commentary in that handbook is not enforceable language. The commentary is opinion, no different than yours or mine.McGraw's NEC Handbook states it plainer than I must have been
Instead of having a plug on the end of the appliance cord, the cord is brought into the outlet box and connected with other methods, like wirenuts.Please refer your understanding of permanently connected ?
Flexible cords and extension cords are not the same thing. Extension cords can be made from flexible cords.I suppose all flexible cords should apply to Article 210.50 if plugged in 24/7/365. Do they? Good luck with that passing acceptance, it's not plausable.
So you are saying flexible cords are an acceptable wiring method?Cords have an allowable section, all to them alone, allowing their use. It's 400.7 specifically. 400.7 nor 400.8 do not make reference to 210.50 as a remedy to not use a cord in-place of or as "substitution".
Right back at you. I appreciate your help in working through this discussion.I still like you though, you seem like a stand-up kinda guy.
If the code requires a receptacle where there is a plug, it should be self-evident that the plug is meant to be inserted into the receptacle.The Commentary in that handbook is not enforceable language. The commentary is opinion, no different than yours or mine.
Try substantiating your opinion with Code.
Well, that is the question. Does it say what you say it says.If the code requires a receptacle where there is a plug, it should be self-evident that the plug is meant to be inserted into the receptacle.