There are listed receptacles that can be connected to flexible conduit and be connected to the inlet....
So how does one install and energize an INLET without a cord?
There are listed receptacles that can be connected to flexible conduit and be connected to the inlet....
So how does one install and energize an INLET without a cord?
There are listed receptacles that can be connected to flexible conduit and be connected to the inlet.
Then I'm back to my certainty of the ambiguity of the present enforceable language you have offered for your opinion. I summarized it back in Post # 358I have posted the code. If you choose to read the words differently, I can't force you to do otherwise.
I'm saying it is a flexible cord at minimum. Whether or not it is also an extension cord I don't know as I'm not sure if we are calling the assembly an extension cord or not (it has been alluded to).Certainly aware of the difference. Which are you implying the supplied cord used in a PowerBridge? I'm certain the supplied cord does not in any manor wirenut to the NM inside the j-box. This is your bias to cite 210.50?
But that is the long-standing code reference cited for appliance applications like this. Perhaps they did not feel the need to state it again.I did not imply that in any way. I implied if 210.50 exists to disallow flexible cords as you are citing, I was claiming the uses not permited of a cord and no where is the reference to 210 to remedy or apply as priority. The WA AHJ did not reference 210 in his note as the remedy to the "claim of substitution of fixed wiring of a structure" of 400.8(1).
Yes. But it does not end there. The inlet also feeds the rest of the stuff that is being used as an extension of the wiring system. The permitted extension wiring methods are listed in Chapter 3. PowerBridge is not one of them.That's it, no not implying a cord should be used as a substitute for premise wiring of a structure. Just you are permitted to use it to EXTEND power from a premise wired receptacle to an INLET. Man, I've repeated that enough right?
If it were not ambiguous, we would not be here. But there should be weight given to a panel of authorities on the subject. I listed a few, including handbooks, but you can search and find untold numbers of the same positions from many other code enforcement authorities, government agencies, books dealing with NEC compliance, etc.Then I'm back to my certainty of the ambiguity of the present enforceable language you have offered for your opinion. I summarized it back in Post # 358
The allusion is really beside the point because of the NRTL product description of "In Wall Electrical Appliance Assembly".I'm saying it is a flexible cord at minimum. Whether or not it is also an extension cord I don't know as I'm not sure if we are calling the assembly an extension cord or not (it has been alluded to).
But I can't find that in the code.The allusion is really beside the point because of the NRTL product description of "In Wall Electrical Appliance Assembly".
As would new Code, or additional or new NRTL documentation.I agree that a formal interpretation would be weightier than most.
110.3 (b)but i can't find that in the code.
I'm saying it is a flexible cord at minimum. Whether or not it is also an extension cord I don't know as I'm not sure if we are calling the assembly an extension cord or not (it has been alluded to).
But that is the long-standing code reference cited for appliance applications like this. Perhaps they did not feel the need to state it again.
Yes. But it does not end there. The inlet also feeds the rest of the stuff that is being used as an extension of the wiring system. The permitted extension wiring methods are listed in Chapter 3. PowerBridge is not one of them.
BTW, if you click on the "A/A" symbol in the editor, you can see the codes to allow typing the stuff for beginning and ending quotes, colors, etc.
Respectfully, the manufacture nor the NEC have any jursidiction of licensing of who or what is required to be installed by a qualified person.
....That being said is it safe to assume this product should not be installed by "untrained persons" ie unlicensed individuals?
Riddle me this.
Powerbridge installed. Small generator outside on path has cord from it that is plugged into PowerBridge's inlet. (and assume under 2008 NEC before the generator malarky started)
So generator, used in a listed manner, connected by listed cord to an inlet.
Would that be acceptable?
Fascinating, the "B" keeps reseting to lower case
There ya go.good gwad, this multiquote thing is more confusing the NEC itself! I don't get it, I'll ask the 10 yr grandson this weekend. Oh he helped with installation of the PowerBridge at his house last year, pretty smart kid said it was as simple as plugging in an extension cord.
okDid you get that? The PowerBridge is supplied with a listed rated code compliant good ol' fashioned AWG14 extension cord.
So is it a part of the branch circuit or not? Seems to change roles depending on which code section needs to be embraced or shunned.Huh, where in C3 does it reference specifically the application of the "parts-of" assembled as an OUTLET installed behind the TV wired inside a j-box to another j-box wired to the backside of the INLET isn't met?
I'm challanged with your assumption, the outlet behind the TV is infact being energized from the premise wiring methods used to wire the outlet through the cord allowed to be (connected) plugged in, to energize the INLET. All this without modification to the premise wiring system! All "parts-of" are connected to C3 wiring methods in the matter of connectivity and energizing per C3.
Not claiming the cord is C3 itself, but is energized from C3 wired receptacle outlet
Where is the bias? Which part(s) of C3 does the connectivity of the parts not uphold?
Justin,
Thanks for dancing around the subject and avoiding the question. The topic of discussion is whether or not this product is NEC compliant. 90.1(c) states the NEC is not for untrained individuals. You have stated, in many posts, that this product should be installed with compliance to the NEC. That being said is it safe to assume this product should not be installed by "untrained persons" ie unlicensed individuals?
Then why are we even worried about it? It is in-wall art. Do you have any accent lighting recommendations?PowerBridge is viewed as a non-electrical ... type installation
I'm sure there are other considerations but two come to mind at the moment:
The branch circuit goes from the last overprotection device to the outlet. If we are saying the PowerBridge receptacle is providing the required outlet then what about the branch circuit conductor size on a 20 amp circuit?
If the cord is somehow excluded but we say the in-wall portion is providing the required receptacle, then the wires in the wall are branch circuit conductors. Overcurrent protection is required at point where conductors receive their supply (the cord connector/inlet point).