Air conditioner compressor

Status
Not open for further replies.

spooky42

Member
I got red tagged for puting a 40 amp circuit breaker on a #10 wire for a ac
compressor. Compressor tag states minimum circuit ampacity 23.2 amps,
minumum circuit breaker 40 amp. Inspector says I need a 40 amp circuit. How do I show him he is wrong ?
 
Politely show the inspector 440.6(A) Exception #1 & 440.22(C).

Chris

Chris's approach would probably be best but you could always politely ask the inspector what section of the code that your installation is in violation of...

Pete
 
Is this an All in one Inspector or Is this person a Electrical only inspector, as they should know this one.
 
I know one that has been inspecting for 20 years and still turns that down.
 
If you put a fused disconnect at the unit the conductors between the panel and the disconnect would have to be sized to the 40 amp breaker.

In this area, a lot of inspectors would still allow wiring to the 40 amp fused disconnect to remain a #10, even though it has actually become a "feeder". It's kind of stretching Art 430 over in Art 440, or a a liberal interpretation of identifying the fusible disconnect as "only a disconnecting means".... not NEC but local practice.
 
If you put a fused disconnect at the unit the conductors between the panel and the disconnect would have to be sized to the 40 amp breaker.

Why is that? If he used a breaker at the unit would you still have to use 40 amp wire from the panel to the disconnect on the unit? Then on the load side he could use #10 wire??

Dan
 
Why is that? If he used a breaker at the unit would you still have to use 40 amp wire from the panel to the disconnect on the unit? Then on the load side he could use #10 wire??

Dan

Read what 440.6(A) says and then read the definition of a branch circuit.

I could go along with Gus that it's splitting hairs, but it is what it is or as Charlie would say, it says what it says.
 
Read what 440.6(A) says and then read the definition of a branch circuit.

I could go along with Gus that it's splitting hairs, but it is what it is or as Charlie would say, it says what it says.

So the Key word is "FINAL" in the BC Defintion? SO the wire from the panel to the disconnect, a fuse or breaker, would have to be 40amp wire?
 
If you put a fused disconnect at the unit the conductors between the panel and the disconnect would have to be sized to the 40 amp breaker.

I don't believe this is correct. Art. 440 relates only the the branch circuit for the air conditioning/refrigeration equipment (440.1.) But Art 440 also says that is "in addition" to the provisions of Art 430 (440.3(A).)

The feeder section of Art 430 says that for a feeder with conductor sizes based on 430.24 (125% of the largest motor plus full load of the other loads) shall have a protective device having a rating or setting "not greater than" the largest rating of the Branch Circuit protective device based on 440.22(A) for a hermetic motor-compressor, plus the sum of the full load for the other motors.

This should allow a 40A feeder c/b with the #10 feeder conductors.
 