blueheels2
Senior Member
- Location
 - Raleigh, NC
 
- Occupation
 - Electrical contractor
 
Mounted a new meter panel combo and I was going to go through the crawl space with a sub panel feeder and 2 separate HVAC ckts.  Realized today that you can't get there from here.  Now I must mount a 200 amp panel in the house and run the feeders through the attic.  My first thought was to derate for 140 degree attic temp but this comes at a significant cost increase and after reading a few threads up here I'm not sure anyone does and I'm not sure the inspectors require it.  I do have an option of going underground and back into the house but it will have over 360 deg of bends so I would have to put a pullbox in the yard and I am trying to avoid that.  What say you?
	
		
			
		
		
	
				
			
				