I need some opinions on the attached PDF load calculation. We were hired to take over a project where they halted construction back in 2006.
The load calculation has a few minor math errors, but most importantly the service is under-designed by it's own accounts and I am trying to see if it is possible to get it to work.
So two questions about the "Optional Dwelling unit Calc".
1) The original designer took the Range VA at 12,000. I typically take them at 8,000. Would I be able to make this change?
2)The original designer took the entire heating load (including the fan) at 65%. I have always taken ONLY the heat at 65%, and the blower fan at 100%. Which way is correct?
I really appreciate any opinions, thanks guys.