I'm looking at an application trying to determine if the secondary of a medium voltage transformer is adequately protected per the NEC.  From what I can tell all of the same rules with MV transformers apply as do with LV transformer the only difference being that the allowed values of protective devices are higher.
The situation I have is a 2500kVa transformer with a 12.47kV delta primary and a 4.16kV wye secondary at 5.46%Z. The primary of the transformer is protected by a 200A fused switch. The secondary of the transformer has (4) different feeder circuit tapped off of the secondary terminals of the transformers landing on (4) individual pieces of equipment. One feeder terminates on a fused switch which feeds another transformer and (3) other feeders go on to feed (3) individual MV motor starters. I'm looking at this application to see if it meets the requuired code and here is what I see:
The primary is adequately protected since the 200A fuse falls within the allowable 300% fuse rating of the 112A full load on the primary of the transformer.
The first thing that I question on the secondary is the fact that the secondary conductors all terminate in diferent locatins. FPN 2 of table 450.3(A) states that if there is no secondary protection on the transformer then secondary protection can consist of six sets of breakers or fuses grouped in one location. Although at each of the 4 location the transformer secondary terminates there are fuses these fuses are not all "in the same location" Since these do not all terminate in one location would this be considered a violation of code?
Secondly the same FPN requires that when protected by multiple fuses on the secondary the total of these fuse ratings shall not exceed the allowed value of a single overcurrent device which for this transformer would be 225% of transformer secondry FLA of 347A or 867A. In this cases the 3 MV motor fuses are 100A, 100A and 170A while the fuesed switch feeding a transformer has a 200A fuse. This gives a combined seconday fuse total of 570A which falls below the allowable total of 867A thus providing the adquate protection. Do you agree?
Lastly I am verifying that the secondary conductors are protected per 240.21(C). With LV conductors I understand that secondary conductors terminating into an OCPD on the secondary must have an ampacity equal to or greater than the OCPD and the "next size up" rule cannot be used. With MV conductors however are the secondary conducotrs allowed to be protected by 240.101(A) and thus be protected by an fuse that has a rating that is 300% of the cable ampacity. For example on of the conducotrs that feeds on of the motors starters is a #6 MV cable in conduit thus having an ampacity of 58A. This cable terminates in a 100A fuse however this 100A fuse falls within the 300% rating of the cables ampacity. Would this conductor be adquately protected. The other cables are #6, #2, and #1. Does the combined ampacity of these cables come into play in regards to the secondary current rating of the transformer?
Thanks for the help!