gar
- Ann Arbor, Michigan
- EE
111128-1000 EST
Last night I removed the power factor correction capacitor, also temperature was colder at about 35 F. The results were TED 8.0 kWh, and power company 7.0 kWh, ratio = 1.14 from 2230 until 0700. Shorter time period than the previous night. The ratio for the previous night with PF capacitor in place was 0.84 .
There is potential for a lot of error in these short time measurements. This points out the difficulty for an ordinary homeowner to determine whether installation of a PF capacitor will save any money.
Using the measured amount of energy over some time period with a highly variable load profile is a very difficult means to evaluate a product such as a PF capacitor. An instantaneous power measurement is a much better method. But this means that the power measuring instrument must perform with adequate accuracy for the intended purpose. I think the TED 1000 system can not.
Just looking at TED 1 hour data for 0000 to 0900 and 11-23-2011 thru 11-28-2011 you can see the effect of the whole house capacitorr at the main panel. Even though there is weather variation ity is clear that TED has a problem. Days 25, 26, 27 are the only ones with the capacitor present.
The capacitor was not connected until after midday on the 24th. Very clear the TED readings were substantially lower during the nights when the power factor correction capacitor was present.
Code:
[FONT=courier new]
no cap no cap cap cap cap no cap
Hour kWh kWh[FONT=Courier New] kWh kWh[FONT=Courier New] kWh kWh
[/FONT][/FONT]
Day----> 23 24 25 26 27 28
0000 1.114 1.004 1.353 1.116 1.160 1.106
0100 1.056 .965 .792 .752 .616 1.015
0200 1.091 .942 .835 .731 .643 1.034
0300 1.064 .987 .828 .726 .672 .976
0400 1.056 1.042 .745 .823 .663 1.007
0500 1.045 1.054 .825 .744 .695 1.077
0600 .976 1.195 .590 .762 .694 1.090
0700 1.486 1.120 .872 1.106 1.424 1.834
0800 2.446 1.578 2.752 1.610 2.149 2.364
[/FONT]