That calculation is invalid.I am afraid you did not read post #244.The current taken by the example induction motor with full load current of 18A driving a fan type load does not exceed 7A at 0.55 p.u voltage.
http://books.google.co.uk/books?id=osa7ldPgUpEC&pg=PA275&lpg=PA275&dq=steinmetz+motor+equivalent+circuit&source=bl&ots=S5NwRKdPmE&sig=uv74AQ-YNxXlZrmgrHu0Tc9HDNo&hl=en&ei=bhLOTvv1L9SR8gP2w-TbDw&sa=X&oi=book_result&ct=result&resnum=1&ved=0CB8Q6AEwAA#v=onepage&q=steinmetz%20motor%20equivalent%20circuit&f=false
Look at Fig 6.6 on page 278 and you might be able to work out why.
What mivey wrote is pretty like the example you gave in post #275 to support your contention.The increase in rotor resistance was meant to drive the rated load at much reduced speed.But here we are discussing about fan type load whose torque requirement is much less at reduced speed.So your objection does not seem relevant.