One (1) duplex receptacle for disposal and dish washer?
hurk27
I think you've got this all wrong.
The definition of a MWBC clearly states it is a single circuit.
The definition of receptacle makes it clear that if a yoke features two devices, then it is a multiple receptacle.
Where are you coming up with two circuits with single receptacles?
A duplex with a disposal on phase A and a dishwasher on phase B is clearly not an individual branch circuit; 210.21(B)(1) does not apply.
So then I guess we don't need to follow 210.7(B) when we use a MWBC to a duplex:?
(B) Multiple Branch Circuits. Where two or more branch
circuits supply devices
or equipment on the same yoke, a
means to simultaneously disconnect the ungrounded conductors
supplying those devices shall be provided at the
point at which the branch circuits originate
iwire
Massachusetts
It is semantics, IMO. The definition does not state it is a single circuit-- where does it say that? Show me the words in the definition that calls it a single circuit.
The "A" makes it so IMO. 'A' is singular is it not?
I already answered that. In the case of a range it is a single circuit.
My bad, sorry.
As Roger stated 210.4 says that a mwbc shall be permitted to be considered as multiple circuits. Yet you say it is a single circuit. Okay--
Exactly, 'shall be permitted to be considered as multiple circuits' IMO that tells us that the NEC considers it a single circuit that in some applications can be considered two circuits. It is not saying that it is two circuits.
I really don't want to argue this any further.
Well I guess we should turn the server off and go home. :eek:hmy::D
david
Pennsylvania
My bad, sorry.
How does 210.23 enter into your discussion on weather it is a single branch circuit or two branch circuits. Feeding a dishwasher and a say a ? HP disposal
John120/240
Olathe, Kansas
For a dishwasher & disposal, I would install one 20 amp circuit. 12 3 from the switch to the
Receptacle. Break the tab on the hot side, constant hot for DW, switched half for disposal.
This arrangement does not constitute a MWBC. Everybody already know this tho.
david
Pennsylvania
What about a kitchen if one 20 amp Mutiwire circuit supplied all the counter top rec. in a kitchen. Or for that matter all of the rec. in a kitchen. Is it one circuit or two? Are you guys saying it?s a code violation to serve the kitchen rec. with one 20 amp multiwire circuit?
George Stolz
Windsor, CO NEC: 2017
Service Manager
Bob said this, but let me reiterate; it says that a MWBC shall be permitted to be considered multiple circuits. This is not the same as saying, "A MWBC shall be considered multiple circuits."
One is voluntary, the other is not. When it is convenient for us to call it "multiple circuits" such as to comply with 210.52(B)(1), then we are permitted to consider it multiple circuits for our ends. Otherwise, it is a single circuit.
In this case, it is a single circuit with a duplex receptacle on it serving two loads.
david
Pennsylvania
Then it clearly is not one branch circuit but two under those conditions correct?
George Stolz
Service Manager
Absolutely not, that's what 210.4(A) is permitting us to do that the definition otherwise would prohibit. Did you watch the excerpt from Mike's video that I posted above?
david
Pennsylvania
Ok what if I add the kitchen lights too this single circuit do I consider both the dish washer an the disposal added together to determine if my equipment exceeds 50% of the 20 amp rating of this single branch circuit? Or am I missing something here.
George Stolz
Service Manager
Ok what if I add the kitchen lights two this single circuit do I consider both the dish washer an the disposal added together to determine if my equipment exceeds 50% of the 20 amp rating of this single branch circuit? Or am I missing something here.
There's no magic to it. If your dishwasher pulled 5A, then you are at less than 50% for the fixed appliances of that portion of the circuit, that leaves you 15A worth of lighting to add if you desire.
ActionDave
Chief Moderator
Licensed Electrician
Well stated and I agree. Two places to plug something in equals multiple.
The "du" in duplex is derived from the French word "duex", meaning two.
david
Pennsylvania
I read 210.21(A) (2) to say the total rating of utilization equipment if it’s a single branch circuit would I not have to add the 5 amp dishwasher to plus the amps for the ? HP disposal?
In other words what would be the difference in applying 210.21(A) to a single pole 12/2 Branch circuit verses a 2 pole 12/3 branch cercuit
George Stolz
Service Manager
I read 210.21(A) (2) to say the total rating of utilization equipment if it?s a single branch circuit would I not have to add the 5 amp dishwasher to plus the amps for the ? HP disposal?
I suppose you could read it that way - if you add the two poles of the breaker that say 20 together to equal 40 - you'll get the same results. ;)
You could look at it any number of ways. Since the rated load of the dishwasher is 5A @ 120V then you could simply figure the load for a 240V circuit, 2.5A.
david
Pennsylvania
I thought the rating of the branch circuit would be determined by the 20 amp Over- current protection.