A duplex is actually two receptacles so each individual receptacle is only receiving 120 volts.
infinity, I agree with duplex is two receptacles, but I don't agree that the two become individual things since both receptacles still is one device and the device is rated at 125V. Am I missing something here? If I am, then in my opinion the duplex recep. should not be marked as 125V rated. It should say 125/250V rated.
Let me explain it this way.
In reply # 28, There is a switch shown on the left side and let's assume sw is rated for 125V, Can you install this sws in a 277V circuit? if the answer is no,, that would be the end of our discussion.
If answer is yes, then we should be able to install a snap on breaker rated 125V for a 277V.
Or why don't we start installing a 125/250V, 1 phase loadcenter with snap on CB's to a 277/480V, 1 phase feeder?
Let's focus on the voltage rating of the duplex recep. device, rather than getting in to 15A or 20A, is it MWBC or not, is the house wife going to be shocked worst by 120V or 240V.
Voltage rating..........., voltage rating..................?????????
Again the question is the 125V rating written on a device that we call it duplex recep. is for the whole device or is it for each recep. in the duplex device.
If the whole device rated at 125V, then it should not be okey to wire it the way was descibed in the OP.