Chapter 9 tables 8 and 9
mshields
Boston, MA
If I were to do a voltage drop calculation I would use Table 8 and plug in the resistance values listed under the column for Copper/Coated/ ohm/kFT. Do you agree that this is the correct source? Or should I be using Table 9?
Assuming I've been using the right table all these years, I believe that voltage drop is a function of resistance only and has nothing to do with reactance. Is that true.
Anyway, what would one use Table 9 for?
Thanks,
Mike
I have never used Table 9 but I guess you could. Most just use the online calculator or use the formula with Table 8.
I have always used a VD method that, at a minimum, took power factor into account. Honestly I can remember using the values from NEC tables only a few times in my entire career.
I use an excel spreadsheet to calculate voltage drop, and I think the values for resistance and reactance that it uses comes from Table 9.
Table 8 is a DC resistance, and it looks like the value for #12 is slightly lower than the AC resistance given in Table 9.
Also, Table 9 (and my spreadsheet) allows you to consider the type of conduit.
So I would use table 9. And I'd put it in a spreadsheet to automate the process, or use one of the online calculators like Dennis suggested.
According to Southwire's Power Cable Manual - when calculating VD for ac circuits, you must consider resistance and reactance as well as power factor of the load.
. . . I believe that voltage drop is a function of resistance only and has nothing to do with reactance. Is that true?
Here I must disagree. I believe that VD through a wire will be equal to the current flowing through it times the overall impedance (resistance and reactance combined). I usually use the "effective Z" column in Table 9 for manual VD calculations (which I try to avoid having to do :happyyes: ).
I agree completely.
Not that I would ever include this in a voltage drop calculation, but a capacitive load could cancel out the inductive reactance of the line. This would be similar to a series resonant circuit. It is even theroetically possible to have more voltage at the load than at the source.