Chapter 9 tables 8 and 9

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
If I were to do a voltage drop calculation I would use Table 8 and plug in the resistance values listed under the column for Copper/Coated/ ohm/kFT. Do you agree that this is the correct source? Or should I be using Table 9?

Assuming I've been using the right table all these years, I believe that voltage drop is a function of resistance only and has nothing to do with reactance. Is that true.

Anyway, what would one use Table 9 for?

Thanks,

Mike
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have never used Table 9 but I guess you could. Most just use the online calculator or use the formula with Table 8.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I have always used a VD method that, at a minimum, took power factor into account. Honestly I can remember using the values from NEC tables only a few times in my entire career.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I use an excel spreadsheet to calculate voltage drop, and I think the values for resistance and reactance that it uses comes from Table 9.

Table 8 is a DC resistance, and it looks like the value for #12 is slightly lower than the AC resistance given in Table 9.

Also, Table 9 (and my spreadsheet) allows you to consider the type of conduit.

So I would use table 9. And I'd put it in a spreadsheet to automate the process, or use one of the online calculators like Dennis suggested.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
According to Southwire's Power Cable Manual - when calculating VD for ac circuits, you must consider resistance and reactance as well as power factor of the load.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
. . . I believe that voltage drop is a function of resistance only and has nothing to do with reactance. Is that true?
Here I must disagree. I believe that VD through a wire will be equal to the current flowing through it times the overall impedance (resistance and reactance combined). I usually use the "effective Z" column in Table 9 for manual VD calculations (which I try to avoid having to do :happyyes: ).
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Here I must disagree. I believe that VD through a wire will be equal to the current flowing through it times the overall impedance (resistance and reactance combined). I usually use the "effective Z" column in Table 9 for manual VD calculations (which I try to avoid having to do :happyyes: ).

I agree completely.

Not that I would ever include this in a voltage drop calculation, but a capacitive load could cancel out the inductive reactance of the line. This would be similar to a series resonant circuit. It is even theroetically possible to have more voltage at the load than at the source.
 