Your rectifier circuit prevents Ia and Ib from existing at the same point in time. I posted a diagram showing Ia and Ib in-phase in a non-rectifier circuit.Are Ia and Ib in phase?
I would suggest the transformer secondary voltages are not synchronized because they have opposite polarities as applied, but they share the same phase. That is, their periodic voltage functions, however derived, all have the same period P and at any time t they have simultaneously advanced t/P over their respective period.You can if you wish but how they flow in terms of phase and magnitude is a consequence of of the applied voltage and load characteristics.
Hanging my hat on it? No. It just had a simple explanation which as we say here, was good enough for government work. And saved a lot of typing.
[ur]http://en.wikipedia.org/wiki/Skin_effect[/url]
emphasis added
And the area surrounding the residential wires would be called ... ... INSULATION! Alternating current flows INSIDE the copper to a depth determined by it's frequency. Not outside. Otherwise insulation would be the most worthless material in the world. It would burn/melt as the power passed through it and you'd get shocked/burned just touching it.
:rotflmao:
Maybe you should read some of those materials instead of just collecting them.
No one is saying that V12 and V34 are not in phase. What has been said is that it is also true that V12 and V43 are phase-opposed. My open-wye example shows that usage is physically valid because we make use of a
Again, the energy travels in the wave. If you do not understand that then you simply need to get your education up to date. Simple examples of peas pushed through a pipe might be used at a very elementary level but it is not a correct representation of how the energy is transported. Those types of examples can actually cause a stumbling block to a better understanding, much like you are faced with now. Time to get rid of your elementary ideas and graduate to something that is more accurate.And the area surrounding the residential wires would be called ... ... INSULATION! Alternating current flows INSIDE the copper to a depth determined by it's frequency. Not outside. Otherwise insulation would be the most worthless material in the world. It would burn/melt as the power passed through it and you'd get shocked/burned just touching it.
I have never said it is not. In fact I usually do so, in my math.You can look at it any way you wish Jim, but it is very logical to define both terminal voltages relative to N--in a consistent fashion.
Good luck with 3-wire delta circuit, if this is really your position.It would be inconsistent to use more than one reference in a circuit,...
I have never siad you were forced to use any specific pronunciation. But I have argued against discussing produce when the OP was about 'utility transformers' and 120/240V services.You say tomato, I say tomahto. That's it..
Not so.Your rectifier circuit prevents Ia and Ib from existing at the same point in time.
Are Ia and Ib not opposite phases?I would suggest the transformer secondary voltages are not synchronized because they have opposite polarities as applied, but they share the same phase. That is, their periodic voltage functions, however derived, all have the same period P and at any time t they have simultaneously advanced t/P over their respective period.
Edit add: FWIW, that applies to the fundamental frequencies of Ia and Ib in 1004 too.
You have physically moved the winding connections, but the relationship of the voltages, V21 &V43 across the open circuit transformer windings does not change.120224-0925 EST
In my post 1293 you ignored responding to the first and main part of the post.
If we use the conventional usage of the labeling of X1 and X2 being one secondary coil with X2 having an associated dot, and the other other coil being X3 and X4 with 4 having the dot, then connect X1 to X3. What is the voltage difference between X2 and X4? In turn is VX2-X1 in-phase or 180 degrees out of phase with VX4-X3?
No. As I told you before, the power flows towards the load as if the wires were a waveguide. The energy flows along both wires towards the load. It travels in the electromagetic field surrounding the wires, not riding in the wires like a line of coal cars traveling back and forth.
Oh please. This is a major technical error on Mivey's part. Are you gonna tell me you think the current travels OUTSIDE the copper as Mivey stated? Pony up Rattus. Is he right or wrong? Should we take a poll? I'll even lead off.SNIPER ATTACK! TAKE COVER NOW!
Nope; they just aren't synchronized either. If you care to do the Fourier analysis; assuming you use the same period P as the transformer's the phase of the fundamental frequencies of Ia and Ib will be the same as the transformer's.Are Ia and Ib not opposite phases?
The physical connections of transformer windings have a direct impact on how the real world operates. Please go ahead and physically wire the rectifier circuit as V12 and V43, let me know how that works for you.
Come on out here, to this part of the real world, where more than 80% of the installed 3-wire deltas are ungrounded.I would ground one corner of the delta (on paper) and call that my reference.
Actually specific single-phase connections that are used to supply residential 120/240V.But today, we are discussing single phase systems.
Hmm, great idea, ignore the subscript methodology you have been promoting for designating voltage references. Maybe someday you will maintain some consistency.X2 tied to X3 would form the common/neutral and it would work just fine. But, we knew that from day one.
I said "on paper". Most if not all simulation programs require a "ground" reference. Quite alright for simulation purposes where we can't get hurt by doing something stupid.Come on out here, to this part of the real world, where more than 80% of the installed 3-wire deltas are ungrounded.
A Fourier series analysis will give you the magnitude of the various harmonics that constitute the waveform.Nope; they just aren't synchronized either. If you care to do the Fourier analysis; assuming you use the same period P as the transformer's the phase of the fundamental frequencies of Ia and Ib will be the same as the transformer's.
Has NOTHING to do with the OP's question. Just more sniping.
Are you saying the fundamental frequency of the currents in 1004 won't have the same phase as the transformer's?A Fourier series analysis will give you the magnitude of the various harmonics that constitute the waveform.
It's something I routinely have to do to analyse the effects of non-linear loads on supply voltage distortion. When we bid for a project I have to commit to not to exceed levels of distortion. And agree to financial consequences for failure to comply with the limits.
That gets your attention.
Credibility Rattus. If you don't know where the current is in the conductor then how can you be an expert on its use. His current description invalidates E=IR. If you don't know how current flows in a conductor then how can you claim to understand the current induced in the secondary. Your ad hominem attack on the challenge of a technical error is dropping your credibility. Right now it implies you think residential current travels through the air. If someone can't understand the current stays in the copper then they'll never understand phase.