Okay, Here is the application. The customer supplied a 500 KVA dry type transformer. 480 volt delta primary, 120/208 wye secondary. Our job was to connect all the raceways and wiring. The secondary load is a very high tech tool for the semi conductor industry. The transformer secondary is to feed a 1200 amp main breaker with 208 volts 3 phase plus the equipment ground. The customer already owned the transformer (new) and requested that it be used for the job.
One of my new electrician's on the job brought up that on a previous job, when using a wye secondary transformer, where no neutral is needed at the load, he was asked by the engineer designing the job not to ground or bond the X0 terminal on the transformer.
I did not do this and we grounded and bonded the transformer as we always do. I stated if we did not do this, there would be no potential to ground on the secondary and would be a dangerous thing to do.
It came up again weeks after the install in the master class the same electrician is enrolled in. The teacher, who is also an inspector said the transformer secondary should not be bonded or grounded if the neutral is not used. I asked my electrician to ask the teacher why? He said he did, but got no answer. The guy said thats just the way you should do it.
I figured someone on the forum may know some reason why these guys would want this done this way. I've never heard of it in my 27 years of business.