Just talked with the smartest man I know. He says in so many words that you CANNOT use trig identities to dump the phase constant!
mmm, rattus. The phase constant 180 deg difference was dumped into the equation when you swapped the leads of the test equipment relative to the winding turn direction. The second measurement taken is of an otherwise identical in every way second winding, induced by the same uniform magnetic field. The only change is of the orientation of the test leads relatve to the winding turn direction. The transformer supplied to you by the factory for testing has two fixed matched windings that have uniform turns in the same direction.
Could you ask your smart friend if creating the 180 phase difference by reversing the leads relative to the winding turn direction is a valid second independent phase or a conventional case available from any one unique phase ?
That is, the arguement includes the facts provided by the transformer itself and not just the on paper statement, sin(wt) != sin(wt + 180).
The facts provided to you by the fixed constant of the transformer's manufacture are two identical matched windings sharing the same iron core and same magnetic field. The 180 deg phase constant difference is added by you when the leads are swapped relative to the winding turn direction. Effectively, looking from the center of the winding and turning your head 180 deg to look at one winding, then the other. Using two points of view (different by 180 deg), rather than looking at the same from one end and seeing that the factory provided two windings both wound in the same direction (seeing what is actually there).
The windings are two voltage sources added in series, the phasors are summed at the output to yield a 240 volt source.
Simply: sin(wt) + sin(wt) = 2sin(wt)
Your view is: sin(wt) + sin(wt + 180) = 0, which is not what is observed at the output.
Somehow you need to add in an extra multiplication by (-1) to cancel out the 180 deg phase shift added by you, by reversing the test leads, during the measuring process.
You are describing the underlying reality, not creating it. That is done for you by the factory and fixed. Take both phasor measurements consistent with the winding turn direction, which is the physical reality provided to you to observe, and sum the phasors because the series connection is the arrangement provided to you to observe. The windings are connected in series as matched identical voltage sources. The facts are provided to you to observe if you have any interest in the underlying physical reality.
Your arguement consistently included the statements 'subtract when I add the winding in series' and 'forget the transformer' as the facts provided by the transformer are inconvenient for you and inconsistent with your arguement. You omit that phi0 = 180 was added by you to the second measurement, by being inconsistent relative to the winding turn direction. The factory provides a second winding to you that is consistent in turn direction.