gar
- Ann Arbor, Michigan
- EE
120309-0809 EST
For those who are arguing that we have simply swapped the meter leads I have the following comments:
If you have really done some circuit analysis, then you understand that the sense (polarity or phase) requires picking a reference point from which to work.
Consider a vacuum tube radio. Typically you would pick the chassis (common, ground, neutral, etc.) as the DC voltage reference point. Plate voltages would be positive relative ground or the tube would not conduct. Grid bias voltage would be negative relative to ground or the tube would be driven into saturation, and if the plate series resistance was low, such as a transformer load, then you would also burn out the tube by overheating the plate.
With a typical DC voltmeter the meter has a scale from 0 to a max. There are few zero-centered meters. To measure the grid bias you would put the positive meter lead on ground and use the negative lead as your probe. But you would know and understand that the meter was reading a negative voltage relative to ground.
With an oscilloscope or typical digital voltmeter you would put the common meter lead on ground and leave it there and directly read + and - from the instrument.
You put the instrument reference lead at the point from where you want to make (reference) your measurement.
In the above vacuum tube example you would not describe the grid bias as positive simply because the analog meter read upscale.
Now consider a 12 V battery with a series load resistance of 10 ohms plus 2 ohms. The 2 ohm end is connected to the battery minus terminal. What is the voltage across the 2 ohm resistor relative to the node between the 10 ohm and 2 ohm resistors? Is it +2 V or is it -2 V? What is the voltage across the 10 ohm resistor relative to the same node? Is it +10 V or -10 V?
Back to the vacuum tube amplifier. Put an AC signal on the grid. Synchronize an oscilloscope to the input signal. Display both the AC input signal (grid voltage) and the AC output signal (plate voltage). Are these two signals "in-phase" or 180 degrees "out-of-phase"?