ramsy
NoFixNoPay Electric
- LA basin, CA
- Service Electrician
My experience with this was during a NECA project in the summer of 2006, while SASCO wired a new 5-story building for CBS studios in west Los Angeles. Under the 2002 code cycle, the commercial inspector failed rough-in (no devices yet), since #12 was bonded to metal boxes with EMT & #10 wire.But doesn't the box bonding pigtail require a #10 if any EGC in the box is a #10?
The inspector did not care that EMT provides sufficient grounding & bonding, nor did he ask for plans, or know if 30A commercial kitchen equipment went on the circuit he failed. There was no code reference on failed inspection notice, just "box-bonding wire doesn't match #10".
However, the inspector missed several other shortcuts that saved the contractor money, and left me with a lasting impression that competitive bids may leverage the inspection process, which must prove code violation before cost of compliance is accrued.
Journeymen are expected to perform, and pressing code issues during production may not be well received. Unless such code violations are recognized as costly liability, project managers are already stressed, and if the apprenticeship failed to remove an argumentative, objectionable, or disruptive character, the foremen are there to make sure that oversight is corrected.Where does it allow reducing from #10 to #12 at any point in the grounding path? It does not. ..Those that do not may get a correction and have to replace the #12 prefab pigtails with #10.