Finite 10, this is beginning to seem like argument just to argue.
1. Surely you won't argue that #12 is insufficient for a 20A circuit.
2. I'm sure I will be corrected if I am wrong about this, but I think the only NEC requirement for VD is that it be held to 3 % in the branch circuit and 5% overall ....and I believe that is only in the FPN which is informational only.
3. It is not electrically necessary to increase the size of the conductors the entire length of the circuit to limit the voltage drop.
4. If it were necessary to increase the size of the entire length of the circuit conductors to 6 or 4 , as you seem to be saying, how would you connect them to a 20A. receptacle? ( or maybe two in a 2 gang box ) I don't think I would know how.
1. Surely you won't argue that #12 is insufficient for a 20A circuit.
2. I'm sure I will be corrected if I am wrong about this, but I think the only NEC requirement for VD is that it be held to 3 % in the branch circuit and 5% overall ....and I believe that is only in the FPN which is informational only.
3. It is not electrically necessary to increase the size of the conductors the entire length of the circuit to limit the voltage drop.
4. If it were necessary to increase the size of the entire length of the circuit conductors to 6 or 4 , as you seem to be saying, how would you connect them to a 20A. receptacle? ( or maybe two in a 2 gang box ) I don't think I would know how.