Nor do I.I don't think that's the predominant answer here at all.
Roger
YesI am resurecting this thread.
Ok I have read what you folks have said and still wonder the following.
SO you cannot use #10nm for a 20 amp circuit? Yes
What about using an existing circuit that is from an Existing Range or dryer and downsizing it for a 15 or 20 amp cicuit and installing the appropriate breaker?
Again... Why not?What about using an existing circuit that is from an Existing Range or dryer and downsizing it for a 15 or 20 amp cicuit and installing the appropriate breaker?
Looking at http://forums.mikeholt.com/showthread.php?t=146402&page=2&p=1417914
You apparrently cannot! I don't agree though.
I guess I did not need to resurrect this particular thread.
Sure you can, you can use #10, #8, #6, or any other larger conductor, even 1000KCMIL if you wish.SO you cannot use #10nm for a 20 amp circuit?
If you had 10-3 I think you could use that on a 20A circuit. If you had 8-3 or 6-3 you could not. The reason is that the ungrounded conductors became larger so the equipment ground must be proportionately larger. If you upsize from #12 to #10, the EGC must be #10, so 10-2 romex is fine. On 8-3 or 6-3 romex, the EGC is #10 which is not large enough for a #8 or #6 conductor.
For 15, 20, and 30 amp circuits, the EGC must be the same size as the ungrounded conductors when you oversize the wire (because the ground and ungrounded are the same size per 250.122). For larger circuit breakers, you have to do the math to see how much larger you need to go. You couldn't legally use 6-3 on a 40A circuit either, but I bet most inspectors wouldn't catch it or care unless the cable run was very long.