With it operating as unrestricted as possible at full speed. 4.8 amps
With it operating with only the the inlet blocked at full speed 3.8 amps
With it operating with only the outlet blocked at full speed 3.7 amps
Demonstrates the real world situation nicely, if I may say so.
As you are probably aware we supply drives mostly for industry and some of these are on large fans. It is common for these to be started against closed dampers.
The fans, being large, have a high inertia. Closing the dampers reduces the load during starting allowing an easier run up.
For those who haven't experienced this, it might seem counter intuitive. Block the outlet thus it has to work harder might be the cause of any such misconception.