Is that PVC supporting the box?
If so, 314.23(F) does not seem to allow this.
(F) Raceway-Supported Enclosures, with Devices, Luminaires,
or Lampholders. An enclosure that contains a
device(s), other than splicing devices, or supports a luminaire(
s), lampholder, or other equipment and is supported by
entering raceways shall not exceed 1650 cm3 (100 in.3) in
size. It shall have threaded entries or have hubs identified for
the purpose. It shall be supported by two or more conduits
threaded wrenchtight into the enclosure or hubs. Each conduit
shall be secured within 450 mm (18 in.) of the enclosure.
My bad, this is why you should never answer from what you remember.
Chris and Derek are correct.
Hopefully the photo is attached.
Does the installation comply with the NEC?
I think the main question is - Can the box be supported by the conduits?
One fix is to drive uni strut behind the box & attach box to strut with a spring nut.
Other fix drive 1/2 or 3/4 rigid with the threads up & screw box on the rigid. Then use the
other knock out for PVC supply.
Buck the schedule 80 is for protection but it has nothing to do with supporting the box. I usually drive a piece of unistrut in the ground or use a 4x4 post.It would have to be schedule 80 PVC. My local supply house in NC does not carry schedule 80 in 3/4 PVC
See post #4Why are you saying PVC is excluded?
	See post #4
Yes, and I was trying to understand the reasoning behind why a single conduit can?t support a device box, but can support a luminaire under conditions. I believe I see the reasoning.Isn't exception 2(E) referencing a luminaire???? That is what exception 2 is about.
See Section 352.12BThat is why I am asking. Do you mean the requirment for the threaded entry?