Just in case you don’t have your code book:
PVC conduit shall not be used under the conditions specified in 352.12 (A) through (F).
-B Support of Luminaires. For the support of luminaires or other equipment not described in 352.10H.
352.10H
-PVC conduit shall be permitted to support nonmetallic conduit bodies not larger than the largest trade size of an entering raceway. These conduit bodies shall not support luminaires or other equipment and shall not contain devices other than splicing devices as permitted by......
PVC conduit shall not be used under the conditions specified in 352.12 (A) through (F).
-B Support of Luminaires. For the support of luminaires or other equipment not described in 352.10H.
352.10H
-PVC conduit shall be permitted to support nonmetallic conduit bodies not larger than the largest trade size of an entering raceway. These conduit bodies shall not support luminaires or other equipment and shall not contain devices other than splicing devices as permitted by......