Outdoor receptacle box

Status
Not open for further replies.

olc

Senior Member
Hopefully the photo is attached.
Does the installation comply with the NEC?
I think the main question is - Can the box be supported by the conduits?
 

Attachments

  • Outdoor Outlet_WC Patio.jpg
    Outdoor Outlet_WC Patio.jpg
    81.5 KB · Views: 2

jumper

Senior Member
Is that PVC supporting the box?

If so, 314.23(F) does not seem to allow this.

(F) Raceway-Supported Enclosures, with Devices, Luminaires,
or Lampholders. An enclosure that contains a
device(s), other than splicing devices, or supports a luminaire(
s), lampholder, or other equipment and is supported by
entering raceways shall not exceed 1650 cm3 (100 in.3) in
size. It shall have threaded entries or have hubs identified for
the purpose. It shall be supported by two or more conduits
threaded wrenchtight into the enclosure or hubs.
Each conduit
shall be secured within 450 mm (18 in.) of the enclosure.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Is that PVC supporting the box?

If so, 314.23(F) does not seem to allow this.

(F) Raceway-Supported Enclosures, with Devices, Luminaires,
or Lampholders. An enclosure that contains a
device(s), other than splicing devices, or supports a luminaire(
s), lampholder, or other equipment and is supported by
entering raceways shall not exceed 1650 cm3 (100 in.3) in
size. It shall have threaded entries or have hubs identified for
the purpose. It shall be supported by two or more conduits
threaded wrenchtight into the enclosure or hubs.
Each conduit
shall be secured within 450 mm (18 in.) of the enclosure.

I agree if that is PVC supporting the box then it is a violation.

Chris
 

John120/240

Senior Member
Location
Olathe, Kansas
Hopefully the photo is attached.
Does the installation comply with the NEC?
I think the main question is - Can the box be supported by the conduits?

One fix is to drive uni strut behind the box & attach box to strut with a spring nut.

Other fix drive 1/2 or 3/4 rigid with the threads up & screw box on the rigid. Then use the

other knock out for PVC supply.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
One fix is to drive uni strut behind the box & attach box to strut with a spring nut.

Other fix drive 1/2 or 3/4 rigid with the threads up & screw box on the rigid. Then use the

other knock out for PVC supply.

They also make a one hole strap that threads into the KO in the back of the box so you could just drive a piece of rigid behind the box too.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It would have to be schedule 80 PVC. My local supply house in NC does not carry schedule 80 in 3/4 PVC
Buck the schedule 80 is for protection but it has nothing to do with supporting the box. I usually drive a piece of unistrut in the ground or use a 4x4 post.

BTW, I think city carries schedule 80-- they used to anyway.
 

resistance

Senior Member
Location
WA
Hold on!!!
How about Ex 2(e):
spacer.gif
The weight supported by any single conduit does not exceed 9 kg (20 lb).
 

olc

Senior Member
Does it make sense to change from rigid galvanized to PVC after the first bend underground?

Is there a minimum ht of the receptacle above ground?


(I'd look the second one up myself but it is 90 out and I want to take the cycle out for a frapacino)
 

resistance

Senior Member
Location
WA
Isn't exception 2(E) referencing a luminaire???? That is what exception 2 is about.
Yes, and I was trying to understand the reasoning behind why a single conduit can?t support a device box, but can support a luminaire under conditions. I believe I see the reasoning.
 