resistance
- WA
@kwired,
Some utilities are the AHJ. Also, In most cases [99.9% of cases]--where the service is involved--the serving utility dictates how electrical equipment should be installed. Technically they are the AHJ up until their ownership stops. Our local inspectors, or another body of authority inspects based on their specifications.
Please note that the structure (Mobile and Manufactured homes) are under HUD?s jurisdiction. Here is what HUD has to say regarding Manufactured homes (in-part):(3) Service equipment installed on themanufactured home in accordance withArticle 230 of the National ElectricalCode, NFPA No. 70?2005, and thefollowing requirements:***** (ii) Exterior equipment, or theenclosure in which it is installed mustbe weatherproof and installed inaccordance with Article 312.2(A) of theNational Electrical Code, NFPA No. 70?2005, and conductors must be suitablefor use in wet locations;
(iii) Each neutral conductor must beconnected to the system groundingconductor on the supply side of themain disconnect in accordance withArticles 250.24, 250.26, and 250.28 ofthe National Electrical Code, NFPA No.70?2005.
