- Illinois
- retired electrician
First I don't use MC, but I was refering to standard MC that does not have an oversized EGC. That is the EGC is sized based on the ampacity of the circuit conductors."Standard" - that probably means the stuff you normally buy. In which case, probably not. But if "standard" means the stuff I normally buy - the yep plenty exists.
It is my opinion that as long as the EGC or part of the EGC is a wire, then 250.122(F) applies and you have to find a way to increase the size of that wire type EGC.Why would there need to be anything in 250.118 about parallel cables. It is discussing what constitutes an equipment grounding conductor.
A quick look at the spec sheets did not show me anything that would change my mind about needing an oversized EGC when these cables are used in paralleMy norm is Okonite CLX. Rockbestos makes similar and as I recall (that's code meaning I woiuld have to check) so does Southwire. I'm sure a search will turn up the link. The spec I use is a corrogated tube type.
So you are talking about the rounding rule in 240.4(B)?Hummm ... You already know all this - my shorthand is just not clear. Over 800A requires tailoring the trip to be under the cable ampacity and the adjustable trip has to be sealed/bolted covers/supervised access.
I still don't understand this one.Above 3 - 750kcmill, the sheath plus the internal grounding conductor is no longer enough to meet the CB size requirement.
ice