I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 5-199. Thanks, Jim Williams
4 Comment:
250.122 Size of Equipment Grounding Conductors.
(B) Increased in Size. Where ungrounded conductors are increased in size from the minimum size that has sufficient ampacity for the intended installation, wire type equipment grounding conductors, where installed, shall be increased in size proportionately according to the circular mil area of the ungrounded conductors.
(B) Increased in Size. If wire type equipment grounding conductor(s)s are present, where ungrounded conductors are increased in size from the minimum size that has sufficient ampacity for the intended installation because of ambient temperature correction factors, exposure to sunlight on a rooftop, adjustments for more than three current carrying conductors, or for reduction in voltage drop, the following calculations shall be made (all areas in circular mils or mm?):
new ungrounded area / original ungrounded area = ratio
original equipment grounding area ? ratio = new equipment grounding area
The new required size of the equipment grounding conductor(s) shall be the next standard size that is equal or greater than the new equipment grounding area.
5 Statement of Problem and Substantiation.
The original text is so chopped up that just displaying the new text is clearer. Suggest that the reasons for increasing size be explicit and that calculation be expressed as a usable formula rather than suggested by the wording.
4 Comment:
250.122 Size of Equipment Grounding Conductors.
(B) Increased in Size. Where ungrounded conductors are increased in size from the minimum size that has sufficient ampacity for the intended installation, wire type equipment grounding conductors, where installed, shall be increased in size proportionately according to the circular mil area of the ungrounded conductors.
(B) Increased in Size. If wire type equipment grounding conductor(s)s are present, where ungrounded conductors are increased in size from the minimum size that has sufficient ampacity for the intended installation because of ambient temperature correction factors, exposure to sunlight on a rooftop, adjustments for more than three current carrying conductors, or for reduction in voltage drop, the following calculations shall be made (all areas in circular mils or mm?):
new ungrounded area / original ungrounded area = ratio
original equipment grounding area ? ratio = new equipment grounding area
The new required size of the equipment grounding conductor(s) shall be the next standard size that is equal or greater than the new equipment grounding area.
5 Statement of Problem and Substantiation.
The original text is so chopped up that just displaying the new text is clearer. Suggest that the reasons for increasing size be explicit and that calculation be expressed as a usable formula rather than suggested by the wording.