Our local inspector required us to move green ground conductors to the neutral bar on a 400 amp ct metered service with back to back 200 amp Sq D panels.Is this necessary with the factory bonding screw installed in ea panel? (120/208 3ph service)
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Our local inspector required us to move green ground conductors to the neutral bar on a 400 amp ct metered service with back to back 200 amp Sq D panels.Is this necessary with the factory bonding screw installed in ea panel? (120/208 3ph service)
You can land the equipment grounds on the neutral bar when the bonding screw is installed if you wish, but you don't have to.

You cannot land the neutrals on the EGC buss.

Your inspector has it backwards.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Our local inspector required us to move green ground conductors to the neutral bar on a 400 amp ct metered service with back to back 200 amp Sq D panels.Is this necessary with the factory bonding screw installed in ea panel? (120/208 3ph service)

What are the green ground conductors actually doing?
 