You can land the equipment grounds on the neutral bar when the bonding screw is installed if you wish, but you don't have to.Our local inspector required us to move green ground conductors to the neutral bar on a 400 amp ct metered service with back to back 200 amp Sq D panels.Is this necessary with the factory bonding screw installed in ea panel? (120/208 3ph service)
Our local inspector required us to move green ground conductors to the neutral bar on a 400 amp ct metered service with back to back 200 amp Sq D panels.Is this necessary with the factory bonding screw installed in ea panel? (120/208 3ph service)
Branch circuit equipment grounds.