OK, so since the storm last week I have spoken to dozens of portable genny owners and not one of them has hooked them up in a code compliant manner. If they ask what they've done wrong, most don't, I try to give them the minimum requirements required by the NEC Here's an outline what I consider to be the minimum requirements. Feel free to comment or add something that I've missed.
1- Breaker interlock between main and backfed CB's
2- Listed inlet box
3- Properly sized backfed CB and conductors.
4- Listed power cord