- Windsor, CO NEC: 2017
- Hospital Master Electrician
I don't see how hot or cold sequence makes any difference on this topic. :?
In fact as long as the meter base is not recessed into a building, you could mount the thing on the side of that building.
How about a pole supporting overhead conductors, with no tap or anything serving any outlet on the pole? Just an intermediate support pole of an overhead span. It is a structure.
Or underground conductors that emerge from the ground are spliced or tapped in an enclosure on a post or other structure but go directly back into the ground and serve no outlets on the post or other structure?
I'm guessing that if I use one of these with a short piece of 1/2" pipe I've built a structure. :roll:
http://www.aifittings.com/catalog/pdf/sections/weatherproof-box-holder.pdf
I would assume the respective weatherproof box would be located downsteam from OCP and whether or not it is a structure would become a mute point.
That is a neat product.....I've never seen them before.
Well, I guess if you use the inspector's theory in the OP's case you're going to put a disconnect there and turn it in to a feeder with an EGC from that point on. I don't think so.:happyno:
Are you referring to conductors before or after the meter?
That seems to me to be the correct, sensible approach. Is that not NEC compliant?Either, but before the meter is usually also before service point and is POCO problem and not ours.
Say you have an installation with multiple buildings or structures. You are supplying an outbuilding with overhead conductors, but the run was long enough it required multiple poles to support the conductors. There is no load at these support poles, just an attachment point to support the overhead conductors. Does each pole need a (service rated) disconnect? I sure hope not. Now if there is a load(s) at a particular pole, then you need a disconnect, but only need to disconnect that load(s), and not the continuation portion of the overhead feeder. Same thing applies if the feeder is underground. If this is incorrect then I have been doing it wrong for years, and so have many others from what I have seen. If there is no load at the separate structure (the pole) then the separate structure is not being served by electric power, it is simply a support for electrical distribution equipment.
And, in a way, while the NEC is "the law", threads like this are "the caselaw", what people actually did or should have done in the real world.I believe "sensible" and "NEC compliant" are not always the same. Hence, the reason for this thread.
I stand corrected.The NEC is not "The Law"
The NEC is a model code to be edited. . .