JCB
Member
- Location
- Canby, Oregon
sorry for not getting back on here sooner, to answer a few of the questions i have read in the posts everyone has provided......the inspector is requiring disconnects at the post on the load side of the meter (2 @ 200amp service rated) as well as 4 wire feeds, there is already a 200amp service rated disconnect mounted at each building on the exterior prior to entrance of the conductors, he has decided that the post is a structure per nec definition which is a stretch in my opinion (how many of us have built or constructed a 6"x8" pt post) and on the inspection report he has actually labeled it as a "support structure", 230.70 (A)(1) is what he cites as the code violation, I personally delivered my appeal to chief clements and notified him that i intend to appeal his decision as well as i already know his opionion, I call it an opinion as he has made no written inperpretation although on one of my initial conversations he informed me that I was the only person who believed this to be a compliant installation, and in my last conversation he informed me that he had dealt with this same situation at least a dozen times in the last 7 years (over a dozen times in the past 7 years to me would indicate a problem which should have been resolved in writing, this makes me seriously question his ablility to do the job he has). I have also spoken the the senior electrical inspector in three jurisdictions who have all agreed that the installation meets code requirements , and have submitted voluntary plan reviews in each jurisdiction which have been approved.