gadfly56
- New Jersey
- Professional Engineer, Fire & Life Safety
So maybe my assumption is wrong. If not for redundancy, why would you run a circuit according to exception 1?
My understanding of the exception is that if you run smaller than 1/0 in parallel, it must meet those conditions. How does that allow you to run smaller than 1/0 if it doesn't meet those exceptions? If you read it to mean that running parallel conductors under 1/0 in general is allowed, but if they feed those items mentioned in exception 1 they must meet those requirements, doesn't that become a design specification, which the NEC isn't supposed to be?
Personally, I don't see anything wrong with a ring circuit in theory. The problem I see is that it's not a wiring style that electricians here would easily identify in use if they came across it in the field. The term "branch circuit" is a visually descriptive name based on the wiring model we use (a tree) and a ring circuit doesn't fit in that model. For instance, in a ring model you wouldn't be allowed to branch out from the ring. Instead, you would have to expand the ring by running two cables from the tap point to the next device and back. Ultimately I think the best argument against using ring circuits in the US is that it would violate 110.8 (only suitable wiring methods are mentioned) and potentially 110.12 (workmanlike manner). Ring circuits are NOT mentioned in the NEC, so are therefore not suitable, and installing one would be unworkmanlike because you'd be violating 110.8.
The problem is the language employed in the exception, the phrase "shall be permitted to be run" does not mean they must be run. To make the installation method mandatory for all sizes under 1/0, it should read "shall be run". The phrase "shall be permitted" doesn't make the action it refers to mandatory and implies that this method must be allowed and also other methods may exist which may or may not be permitted. Words have meaning, and the Technical Committe should know better.