TrickleCharge
Member
- Location
- CA
Just seeing what everyone thinks about this installation of the a/c unit in the electrical room. I have a large project with about 7 electrical rooms....i noticed yesterday that they were installing these units in each. The XMFR is about 7" off the wall. I know that the condensate will be pumped and going up along with any other piping. Now the question that i have is that per section 110.26 (F) states that the dedicated space is the width and depth of the equipment. The XMFR being 7" off the wall does not interfere with the condensate line, however the complete unit itself is about 10"-12" in depth so this would encroach into that space just barely. What does everyone think? (see attached pics)



